0 members (), 109 guests, and 16 robots.
AKMASTER:
Per HotLine1's post:
No, the bond strap or field installed compliant conductor ONLY bonds the enclosure!
The neutral (XO) must have a compliant GEC. (Rod(s); steel;Ufer;etc.)
The Attached Drawings may be of assistance:
Fig. 1: Front View of Transformer - Details of Lead Terminations.
Fig. 2: Top View of same Transformer.
a.: GEC runs out the back of the Transformer;
b.: Primary Feeders enter on the Right-Side of Transformer;
c.: Secondary Feeders exit on the Left-Side of Transformer;
d.: 3-Terminal Lug with Green Bolt (connected to XO Lug via System Bonding Jumper) is Physically Bonded to the Transformer Enclosure.
Fig. 3: Transformer Winding Connections Schematic, with OCPDs and SDS Panelboard.
Figure #3 Notes:
1.: On the Secondary side's Connections, Terminal "XO would be physically located at the "Dot" above the Green Grounding Bus.
2.: The "Ground Symbols" on the Primary and Secondary sides, are Physical Connections to the Transformer's Enclosure. These Terminations may be either a Factory-Installed Jumper, or a Field-Installed Lug.
These Drawings, along with many others, may be found at the Technical Reference Section of ECN.
--Scott (EE)
Workgear for Electricians
Scott:
As always, Thank You for the added info.
Any time John!!!
--Scott (EE)
Thank you very much for your time and feedback!
regards
Greg
Don't drive and TEXT! Drive now TALK LATER!