Rule 26-256 #209669
04/16/13 10:04 PM
04/16/13 10:04 PM
S
Sparkologist  Offline OP
New Member
Joined: Apr 2012
Posts: 7
Toronto ,Ontario, Canada
This rule relates to overcurrent protection for dry-type transformer circuit rated at 750volts or less. 125% issued for the guide with regard to the secondary side if the primary supply is set at not more than 300 %. the rule 26-254 speaks to 9amps more or less for liquid filed units. Why does the supplieer charts list 250% of the primary FLA or the next size smallee and quotes rule 26-254 and Nec.450.3. Is the chart correct? I don't tink so.

Tools for Electricians:
Re: Rule 26-256 [Re: Sparkologist] #209676
04/17/13 12:14 PM
04/17/13 12:14 PM
T
twh  Offline
Member
Joined: Mar 2004
Posts: 946
Regina, Sask.
If it's a dry transformer, the reference to CEC 26-254 is wrong or refers to a previous edition. The 250% doesn't come from our code but the manufacturer can specify a lower percentage. Maybe 250% comes from the NEC.

Re: Rule 26-256 [Re: Sparkologist] #209683
04/17/13 06:55 PM
04/17/13 06:55 PM
T
twh  Offline
Member
Joined: Mar 2004
Posts: 946
Regina, Sask.
Originally Posted by Sparkologist
My reference to rule 26-254 with regard to sub.(5)a and b is up to date and was to show what the reference was that the Bussman catalogue used. The text from the NEC 450.3 was almost the same as the Canadian code 25th edition 2012. The are saying that if the primary and secondary do not have thermal protection use 250% and if the primary and secondary do have thermal protection and the impedance of the transformer is 6 ohms or less use 125% of the FLA. There chart shows for the primary max fuse, use 250% and for secondary use 167% or 125% depending on the more or less 9 amp rule. My point is that for dry type less than 750v the 9 amp rule does not apply and their pecentages for protecton is wrong.


26-254 once dealt with all transformers and 26-256 dealt with wire size for transformers. Or, are you saying that the Bussman catalogue refers directly to 26-254(5)? Anyway, if you don't like their catalogue, throw it away.

Re: Rule 26-256 [Re: Sparkologist] #209686
04/17/13 11:26 PM
04/17/13 11:26 PM
S
Sparkologist  Offline OP
New Member
Joined: Apr 2012
Posts: 7
Toronto ,Ontario, Canada
ok


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,109 Are you busy
185,564 Re: Forum
174,879 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 15 (0.004s) Memory: 0.9596 MB (Peak: 1.0928 MB) Zlib enabled. Server Time: 2018-07-18 06:21:09 UTC