2012 NEC 2012(A) #209056
03/04/13 10:51 PM
03/04/13 10:51 PM
B
BigB  Offline OP
Member
Joined: Mar 2004
Posts: 721
Tucson, AZ USA
Article 210.12 (2012) Arc Fault Circuit Interrupter Protection does not include bathrooms, kitchens or garages in the list of required circuits to be protected, but it does list “or similar areas”. Does this mean that the lighting circuits in the garage, bathroom and kitchen do not need to be AFCI protected? Does this also mean that any kitchen receptacle circuits that do not serve the countertops need not be AFCI protected, even if they are not GFCI protected (i.e. dishwasher, fridge, range hood microwave)?

2017 / 2014 NEC & Related Books and Study Guides
Re: 2012 NEC 2012(A) [Re: BigB] #209062
03/05/13 01:23 AM
03/05/13 01:23 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
That is the way I read it. That multiwire under the sink for the dish washer and disposal is still OK.


Greg Fretwell
Re: 2012 NEC 2012(A) [Re: BigB] #209071
03/06/13 12:51 AM
03/06/13 12:51 AM
B
BigB  Offline OP
Member
Joined: Mar 2004
Posts: 721
Tucson, AZ USA
Thanks. We just adopted the 08 & 12 in one swoop, got some catching up to do.

Re: 2012 NEC 2012(A) [Re: BigB] #209072
03/06/13 02:20 AM
03/06/13 02:20 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
I was at lunch with a Leviton rep who had one of the elusive AFCI devices a week or so ago and he says they believe the length restriction to the first device will be gone in 2014 and we will be able to drop a device in the first box to protect the circuit downstream


Greg Fretwell
Re: 2012 NEC 2012(A) [Re: BigB] #209080
03/06/13 09:44 AM
03/06/13 09:44 AM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
What about lights in detached garage? As BigB said, would they have to be on a AFCI? As some of you know, that code section that states "AND SIMILAR AREAS" is not a very good way to write that code section. Plus AFCI's were originally to protect just the bedroom receptacles from those annoying extension cords.

Re: 2012 NEC 2012(A) [Re: BigB] #209082
03/06/13 10:37 AM
03/06/13 10:37 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,916
Brick, NJ USA
Regarding a 'detached' garage...NO AFCI requirements. Receptacles are required to be GFI, and that's it.

Argue that if the garage is attached....the word 'garage' is not mentioned, nor would a lot of us think it is 'similsr' to the areas listed. Now, for some of us that think 'ahead', what if the garage is used for a 'play area' like with a ping-pong table??

Evenyually, IMHO, a house will soon be ALL AFCI &/or GFI.



John
Re: 2012 NEC 2012(A) [Re: BigB] #209083
03/06/13 10:38 AM
03/06/13 10:38 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,916
Brick, NJ USA
Greg:
Yes, the elusive AFCI device is around. I requested a 'sample' two weeks ago, but to date nothing.


John
Re: 2012 NEC 2012(A) [Re: BigB] #209143
03/10/13 11:21 AM
03/10/13 11:21 AM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
John,

I agree that AFCI is not required in a garage and I also foresee AFCI and GFCI will be required for the whole house. I am still not "sold" on the idea that AFCI is a stable product. I haven't used any of them yet, but I still hear a lot of EC's complaining about them.

Re: 2012 NEC 2012(A) [Re: BigB] #209145
03/10/13 11:59 AM
03/10/13 11:59 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,916
Brick, NJ USA
Still waiting for a reply on IF a sample of the 'device' is available. I'll look in the 'big-box' store next time I'm in there.


John
Re: 2012 NEC 2012(A) [Re: BigB] #209186
03/14/13 12:44 AM
03/14/13 12:44 AM
B
BigB  Offline OP
Member
Joined: Mar 2004
Posts: 721
Tucson, AZ USA
Another location has come up. 120 volt air handler in the attic. Very common here, and they are all plug and cord connected as well.

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 20
Potseal 13
Popular Topics(Views)
243,527 Are you busy
180,327 Re: Forum
170,819 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.048s Queries: 16 (0.005s) Memory: 1.0242 MB (Peak: 1.2062 MB) Zlib enabled. Server Time: 2018-01-17 20:08:19 UTC