2012 NEC 2012(A) #209056 03/04/13 10:51 PM
Joined: Mar 2004
Posts: 774
B
BigB Offline OP
Member
Article 210.12 (2012) Arc Fault Circuit Interrupter Protection does not include bathrooms, kitchens or garages in the list of required circuits to be protected, but it does list “or similar areas”. Does this mean that the lighting circuits in the garage, bathroom and kitchen do not need to be AFCI protected? Does this also mean that any kitchen receptacle circuits that do not serve the countertops need not be AFCI protected, even if they are not GFCI protected (i.e. dishwasher, fridge, range hood microwave)?

2017 / 2014 NEC & Related Books and Study Guides
Re: 2012 NEC 2012(A) [Re: BigB] #209062 03/05/13 01:23 AM
Joined: Jul 2004
Posts: 9,547
G
gfretwell Offline
Member
That is the way I read it. That multiwire under the sink for the dish washer and disposal is still OK.


Greg Fretwell
Re: 2012 NEC 2012(A) [Re: BigB] #209071 03/06/13 12:51 AM
Joined: Mar 2004
Posts: 774
B
BigB Offline OP
Member
Thanks. We just adopted the 08 & 12 in one swoop, got some catching up to do.

Re: 2012 NEC 2012(A) [Re: BigB] #209072 03/06/13 02:20 AM
Joined: Jul 2004
Posts: 9,547
G
gfretwell Offline
Member
I was at lunch with a Leviton rep who had one of the elusive AFCI devices a week or so ago and he says they believe the length restriction to the first device will be gone in 2014 and we will be able to drop a device in the first box to protect the circuit downstream


Greg Fretwell
Re: 2012 NEC 2012(A) [Re: BigB] #209080 03/06/13 09:44 AM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline
Member
What about lights in detached garage? As BigB said, would they have to be on a AFCI? As some of you know, that code section that states "AND SIMILAR AREAS" is not a very good way to write that code section. Plus AFCI's were originally to protect just the bedroom receptacles from those annoying extension cords.

Re: 2012 NEC 2012(A) [Re: BigB] #209082 03/06/13 10:37 AM
Joined: Apr 2002
Posts: 7,220
HotLine1 Offline
Member
Regarding a 'detached' garage...NO AFCI requirements. Receptacles are required to be GFI, and that's it.

Argue that if the garage is attached....the word 'garage' is not mentioned, nor would a lot of us think it is 'similsr' to the areas listed. Now, for some of us that think 'ahead', what if the garage is used for a 'play area' like with a ping-pong table??

Evenyually, IMHO, a house will soon be ALL AFCI &/or GFI.



John
Re: 2012 NEC 2012(A) [Re: BigB] #209083 03/06/13 10:38 AM
Joined: Apr 2002
Posts: 7,220
HotLine1 Offline
Member
Greg:
Yes, the elusive AFCI device is around. I requested a 'sample' two weeks ago, but to date nothing.


John
Re: 2012 NEC 2012(A) [Re: BigB] #209143 03/10/13 11:21 AM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline
Member
John,

I agree that AFCI is not required in a garage and I also foresee AFCI and GFCI will be required for the whole house. I am still not "sold" on the idea that AFCI is a stable product. I haven't used any of them yet, but I still hear a lot of EC's complaining about them.

Re: 2012 NEC 2012(A) [Re: BigB] #209145 03/10/13 11:59 AM
Joined: Apr 2002
Posts: 7,220
HotLine1 Offline
Member
Still waiting for a reply on IF a sample of the 'device' is available. I'll look in the 'big-box' store next time I'm in there.


John
Re: 2012 NEC 2012(A) [Re: BigB] #209186 03/14/13 12:44 AM
Joined: Mar 2004
Posts: 774
B
BigB Offline OP
Member
Another location has come up. 120 volt air handler in the attic. Very common here, and they are all plug and cord connected as well.

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,256 Are you busy
206,143 Re: Forum
194,135 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3