ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 779 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Nov 2002
Posts: 244
W
wewire2 Offline OP
Member
250.66 (A) "Where the grounding electrode conductor is connected to rod, pipe, or plate electrodes as permitted in 250.52 (A)(5) or (A)(7),that portion of the conductor that is the sole connection to the grounding electrode shall not be required to be larger than 6 AWG copper wire or 4 AWG aluminum wire." Could that be interpreted as the #6 can be the only conductor attached to the ground rod in order to qualify downsizing the conductor? The sizing rules for jumpering to other ground sources are clear but let's say there's a cable TV ground or secondary electrode conductor terminated on the same rod from a meter added to the same service. Could that be interpreted as infringing on the "sole connection" since there is more than one connection at the rod? I think no but just checking.

Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Jul 2004
Posts: 10,043
Likes: 37
G
Member
I think no too. The cable co and telco connection is not a GEC.


Greg Fretwell
Joined: Feb 2002
Posts: 2,233
H
Member
If I am understanding this question, there is the ruling for the inter-system bonding terminal which allows the telco and CATV people to hook into the electric GEC. They use to just clamp to the #6 cu going to the ground rod.

Joined: Jul 2004
Posts: 10,043
Likes: 37
G
Member
In 2011 250.94(2) got more specific

Quote
(2) Consist of a set of terminals with the capacity for connection
of not less than three intersystem bonding conductors.


Greg Fretwell
Joined: Oct 2000
Posts: 5,393
S
Member
Pre-intersystem bonding block (bar? , term strip?) saw a lotta wierd ph & ca GEC 'means of attachment' to GEC's

Most of the ahj's i know weren't particularly bothered by it all, mostly a 'ah, geez, those ph guys again' sort of 'tude....

~S~

Joined: Jul 2004
Posts: 10,043
Likes: 37
G
Member
You are lucky if any of the trunk slammers we call "techs" make the connection to the service grounding electrode system at all. Satellite guys seem to be the worst. They drive that 3' rod attach a #10 to the dish and call it done.
I ended up just starting over on mine with a real rod and a fat wire to the GES.


Greg Fretwell
Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
Over the years there have been a lot of tele/cctv/etc bonds & grounds that were interesting, funny & excersizes of the imagination. The worst were the pipe clapms on PVC and SEU.

Multiple rods? What do you mean they have to be 'bonded' together? Why do I need a 'full size' rod?? That perforated metal strap & 1/4-20 bolt are tight around the meter pan!! The list can go on....


John
Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Oct 2000
Posts: 5,393
S
Member
yeah, one can really tell some fundamental theory isn't understood all that well out there

one thing i've seen the poco have conniptions over are these clamps that go on the corner of a meter face (the cover over the glass meter itself)

they are little clamps about 1"x1" , manufactured specifically for clamping to a meter face

it amazes me that one utility would actually incorporate a specific widget the other sees as a complete intrusion

i just dunno, maybe they should do lunch?

~S~


Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
PSE&G here in NJ really gets very upset with anything attached to their metering equipment. There's some gizmo that attaches to the meter pan that really had them rocking.

I'll look for a pic in my files.


John
Joined: Feb 2002
Posts: 2,233
H
Member
A lot of guys around here would tie their ground to the hub on top of the meter pan. They would use those copper ground straps.


Link Copied to Clipboard