Saw this on Mike Holt's Facebook AFCI Receptacle #208669
02/05/13 12:08 PM
02/05/13 12:08 PM
dougwells  Offline
OP
Member
Joined: May 2003
Posts: 1,142
kamloops BC Canada

Last edited by dougwells; 02/05/13 12:49 PM.
Work Gear for Electricians and the Trades
Re: Saw this on Mile Holt's Facebook Page [Re: dougwells] #208670
02/05/13 12:25 PM
02/05/13 12:25 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,180
Estero,Fl,usa
Holy Grail Batman!
The AFCI device.


Greg Fretwell
Re: Saw this on Mike Holt's Facebook AFCI Receptacle [Re: dougwells] #208671
02/05/13 01:16 PM
02/05/13 01:16 PM
K
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
Looks to be right around $40.00, so no surprise there. Hopefully a little less at actual wholesale from the local supply house, but I'm guessing not by much.

AFCI Receptacle

Re: Saw this on Mike Holt's Facebook AFCI Receptacle [Re: dougwells] #208672
02/05/13 02:26 PM
02/05/13 02:26 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,926
Brick, NJ USA
Interesting, it finally seems to be here. I just sent them an email inquiring if any samples are available for AHJs and Instructors.

Thanks for the news and the link.


John
Re: Saw this on Mike Holt's Facebook AFCI Receptacle [Re: dougwells] #208674
02/05/13 05:33 PM
02/05/13 05:33 PM
Theelectrikid  Offline
Member
Joined: Apr 2004
Posts: 810
Levittown, PA
You mean I don't have to turn a neat panel into a spaghetti factory anymore Wahoo!!

Only problem I could see with this is it would technically leave the home run still vulnerable.

Last edited by Theelectrikid; 02/05/13 05:37 PM.

Is there anyone on board who knows how to fly a plane?
Re: Saw this on Mike Holt's Facebook AFCI Receptacle [Re: dougwells] #208676
02/05/13 07:08 PM
02/05/13 07:08 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,180
Estero,Fl,usa
210.12(A) ex1 covers that

Quote
Exception No. 1: If RMC, IMC, EMT, Type MC, or steel
armored Type AC cables meeting the requirements of
250.118 and metal outlet and junction boxes are installed
for the portion of the branch circuit between the branchcircuit
overcurrent device and the first outlet, it shall be
permitted to install an outlet branch-circuit type AFCI at
the first outlet to provide protection for the remaining portion
of the branch circuit.


Greg Fretwell
Re: Saw this on Mike Holt's Facebook AFCI Receptacle [Re: dougwells] #208677
02/05/13 07:37 PM
02/05/13 07:37 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,926
Brick, NJ USA
Backdoor conformance with 210.12 (A) ex 1 would be to install one of these Leviton devices in a 4Sq adjacent to the panel, with a compliant wiring method from the panel to the 4Sq. Now, compare the $$$ of the 'device' and an AFCI CB.


John
Re: Saw this on Mike Holt's Facebook AFCI Receptacle [Re: dougwells] #208680
02/05/13 09:07 PM
02/05/13 09:07 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,180
Estero,Fl,usa
I think it only makes sense for rehab or renovation in a house that has a pre AFCI style panel that you don't want to replace. (Zinsco or something)
I am surprised these are not dead front. If you are just putting in a few circuits that need to be AFCI, this makes a lot of sense. I imagine you could get 2 in a deep 4x4 or 4 11/16 box. That might be enough for a small addition or a basement remodel.
Prior to this you were running a feeder to a new style sub panel that you could buy AFCI breakers for.


Greg Fretwell
Re: Saw this on Mike Holt's Facebook AFCI Receptacle [Re: dougwells] #208693
02/06/13 05:17 PM
02/06/13 05:17 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,264
Fullerton, CA USA

I find it sort of odd that it's "commercial grade", and the requirements for both AFCI and TR are limited to residential use.

Doesn't say much for their residential grade devices, does it smile

Re: Saw this on Mike Holt's Facebook AFCI Receptacle [Re: dougwells] #208694
02/06/13 09:11 PM
02/06/13 09:11 PM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
electure...

Commercial Grade = Pricing/ Marketing 'Plateau.'

The heftier quality of componentry is simply consequential to that 'positioning.'



Tesla
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Admin
Admin
NY, USA
Posts: 3,490
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 8
Popular Topics(Views)
244,049 Are you busy
181,039 Re: Forum
171,282 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.038s Queries: 16 (0.004s) Memory: 1.0271 MB (Peak: 1.2105 MB) Zlib enabled. Server Time: 2018-02-22 07:13:49 UTC