ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Recent Posts
VFD MotorFeeders
by gfretwell. 10/19/17 01:02 AM
Generator Cable Sizing
by brsele. 10/18/17 07:39 PM
What do you do?
by gfretwell. 10/17/17 01:08 AM
Good ol' copper pipe in the fuse holder trick
by HotLine1. 10/16/17 07:16 PM
Another generator question
by HotLine1. 10/16/17 07:02 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
241,407 Are you busy
177,375 Re: Forum
168,976 Need opinion
Who's Online Now
0 registered members (), 39 guests, and 11 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
Page 1 of 2 1 2
#208669 - 02/05/13 01:08 PM Saw this on Mike Holt's Facebook AFCI Receptacle  
dougwells  Offline


Member
Joined: May 2003
Posts: 1,140
kamloops BC Canada

Last edited by dougwells; 02/05/13 01:49 PM.

Work Gear for Electricians and the Trades

#208670 - 02/05/13 01:25 PM Re: Saw this on Mile Holt's Facebook Page [Re: dougwells]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,123
Estero,Fl,usa
Holy Grail Batman!
The AFCI device.


Greg Fretwell

#208671 - 02/05/13 02:16 PM Re: Saw this on Mike Holt's Facebook AFCI Receptacle [Re: dougwells]  
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
Looks to be right around $40.00, so no surprise there. Hopefully a little less at actual wholesale from the local supply house, but I'm guessing not by much.

AFCI Receptacle


#208672 - 02/05/13 03:26 PM Re: Saw this on Mike Holt's Facebook AFCI Receptacle [Re: dougwells]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,872
Brick, NJ USA
Interesting, it finally seems to be here. I just sent them an email inquiring if any samples are available for AHJs and Instructors.

Thanks for the news and the link.


John

#208674 - 02/05/13 06:33 PM Re: Saw this on Mike Holt's Facebook AFCI Receptacle [Re: dougwells]  
Theelectrikid  Offline
Member
Joined: Apr 2004
Posts: 810
Levittown, PA
You mean I don't have to turn a neat panel into a spaghetti factory anymore Wahoo!!

Only problem I could see with this is it would technically leave the home run still vulnerable.

Last edited by Theelectrikid; 02/05/13 06:37 PM.

Is there anyone on board who knows how to fly a plane?

#208676 - 02/05/13 08:08 PM Re: Saw this on Mike Holt's Facebook AFCI Receptacle [Re: dougwells]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,123
Estero,Fl,usa
210.12(A) ex1 covers that

Quote
Exception No. 1: If RMC, IMC, EMT, Type MC, or steel
armored Type AC cables meeting the requirements of
250.118 and metal outlet and junction boxes are installed
for the portion of the branch circuit between the branchcircuit
overcurrent device and the first outlet, it shall be
permitted to install an outlet branch-circuit type AFCI at
the first outlet to provide protection for the remaining portion
of the branch circuit.


Greg Fretwell

#208677 - 02/05/13 08:37 PM Re: Saw this on Mike Holt's Facebook AFCI Receptacle [Re: dougwells]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,872
Brick, NJ USA
Backdoor conformance with 210.12 (A) ex 1 would be to install one of these Leviton devices in a 4Sq adjacent to the panel, with a compliant wiring method from the panel to the 4Sq. Now, compare the $$$ of the 'device' and an AFCI CB.


John

#208680 - 02/05/13 10:07 PM Re: Saw this on Mike Holt's Facebook AFCI Receptacle [Re: dougwells]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,123
Estero,Fl,usa
I think it only makes sense for rehab or renovation in a house that has a pre AFCI style panel that you don't want to replace. (Zinsco or something)
I am surprised these are not dead front. If you are just putting in a few circuits that need to be AFCI, this makes a lot of sense. I imagine you could get 2 in a deep 4x4 or 4 11/16 box. That might be enough for a small addition or a basement remodel.
Prior to this you were running a feeder to a new style sub panel that you could buy AFCI breakers for.


Greg Fretwell

#208693 - 02/06/13 06:17 PM Re: Saw this on Mike Holt's Facebook AFCI Receptacle [Re: dougwells]  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,262
Fullerton, CA USA

I find it sort of odd that it's "commercial grade", and the requirements for both AFCI and TR are limited to residential use.

Doesn't say much for their residential grade devices, does it smile


#208694 - 02/06/13 10:11 PM Re: Saw this on Mike Holt's Facebook AFCI Receptacle [Re: dougwells]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
electure...

Commercial Grade = Pricing/ Marketing 'Plateau.'

The heftier quality of componentry is simply consequential to that 'positioning.'



Tesla

Page 1 of 2 1 2

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.025s Queries: 16 (0.004s) Memory: 0.8222 MB (Peak: 1.0035 MB) Zlib enabled. Server Time: 2017-10-20 12:27:41 UTC