Example Panel Schedules - Per Thread At NEC Area #208150
12/29/12 11:06 PM
12/29/12 11:06 PM
Scott35  Offline OP
Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,720
Anaheim, CA. USA
In regard to the Thread Size Feeder?, located at the NEC Forum Area, I have compiled and attached (4) Panel Schedules for example descriptions.

Basic Descriptions:

a. System = 208Y/120V 3 Phase 4 Wire,
b. Panelboard(s) are 30 Space, 200 Amp, 3 Phase 4 Wire, MLO,
c. Loads are as described in the Thread, and per each Schedule's notes.

Post #1 of 2:
Example #1 (PSCHED 1M): 30 Space Panelboard with L-L VA figured as Amperes x 208 / 2; Neutral Load from L-N Circuitry only.

and,

Example #2 (PSCHED 2M): 30 Space Panelboard with L-L VA figured as Amperes x 120; Neutral Load from L-N Circuitry only.

--Scott (EE)



Attached Files
PSCHED_1M_ECN_121229.pdf (44 downloads)
PSCHED_2M_ECN_121229.pdf (18 downloads)
Example #1: L-L Load VA = I x 208; Neutral Load added from L-N Circuits Only.
Last edited by Scott35; 12/29/12 11:08 PM.

Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Re: Example Panel Schedules - Per Thread At NEC Area [Re: Scott35] #208151
12/29/12 11:12 PM
12/29/12 11:12 PM
Scott35  Offline OP
Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,720
Anaheim, CA. USA
Post #2 of 2 - examples #3 and #4:

In regard to the Thread Size Feeder?, located at the NEC Forum Area, I have compiled and attached (4) Panel Schedules for example descriptions.

Basic Descriptions:

a. System = 208Y/120V 3 Phase 4 Wire,
b. Panelboard(s) are 30 Space, 200 Amp, 3 Phase 4 Wire, MLO,
c. Loads are as described in the Thread, and per each Schedule's notes.

Post #2 of 2:
Example #3 (PSCHED 3M): 30 Space Panelboard with L-L VA figured as Amperes x 208 / 2; Neutral Load from ALL Circuits.

and,

Example #4 (PSCHED 4M): 30 Space Panelboard with L-L VA figured as Amperes x 120; Neutral Load from ALL Circuits.

--Scott (EE)


Attached Files
PSCHED_3M_ECN_121229.pdf (23 downloads)
PSCHED_4M_ECN_121229.pdf (12 downloads)

Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
256,961 Are you busy
192,847 Re: Forum
182,459 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 17 (0.004s) Memory: 0.9463 MB (Peak: 1.0665 MB) Zlib enabled. Server Time: 2019-07-15 20:17:04 UTC