Fluorescent Lighting calculations #207932 12/09/12 08:10 PM
Joined: Apr 2003
Posts: 362
Obsaleet Offline OP
Member
I must be getting old!! I connot seem to remember how to find the wattage of a fluorescent fixture. 2 f40's with a magnetic ballast? I think .51 for the ballast.


Ob


Choose your customers, don't let them choose you.
Work Gear for Electricians and the Trades
Re: Fluorescent Lighting calculations [Re: Obsaleet] #207939 12/10/12 12:08 AM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline
Member
It is based on tha ballast rating. If the fixture info is in front of me, I go to manufacters website and find a similar ballast and pad my numbers to be on the safe side


"Live Awesome!" - Kevin Carosa
Re: Fluorescent Lighting calculations [Re: Obsaleet] #207941 12/10/12 04:01 AM
Joined: Jul 2004
Posts: 9,526
G
gfretwell Online Content
Member
I think there is some safety margin built into that "40w".
When I put my clamp on a shop lite fixture with to F40CWs in it I actually get less than 80w, ballast and all.

Someone point out it might just be the meter is not handling the wave form properly tho.


Greg Fretwell
Re: Fluorescent Lighting calculations [Re: gfretwell] #207942 12/10/12 05:10 AM
Joined: Jul 2007
Posts: 1,335
S
sparkyinak Offline
Member
According to the GE Lighting Institute, the watt rating of the bulbs has nothing to do with the draw of the fixture. Hence, use the ballast rating

Last edited by sparkyinak; 12/10/12 05:11 AM.

"Live Awesome!" - Kevin Carosa
Re: Fluorescent Lighting calculations [Re: Obsaleet] #207992 12/16/12 03:15 PM
Joined: Apr 2003
Posts: 362
Obsaleet Offline OP
Member
This is why I am confused. I thought that you add the ballast to the lamps and thats your total. Then I googled just to see and found so many different ways and none ended with the same result.


Choose your customers, don't let them choose you.
Re: Fluorescent Lighting calculations [Re: Obsaleet] #207993 12/16/12 04:40 PM
Joined: Dec 2012
Posts: 2
H
HTSR77 Offline
New Member
I agree with SparkinAK. When determining the size of the connected load or branch circuit for lighting, the ballast input in watts is used.

Re: Fluorescent Lighting calculations [Re: Obsaleet] #207998 12/17/12 12:33 AM
Joined: Apr 2002
Posts: 7,209
HotLine1 Offline
Member
Ballast data is used for actual lighting connected load calcs. Using the bulb wattage (2x40, 4x32,) can be used for a 'ballpark' figurre, which will be higher most of the time, than actual.

The same applies for HID lighting, use ballast data, not bulb wattage.


John
Re: Fluorescent Lighting calculations [Re: HotLine1] #208000 12/17/12 07:17 AM
Joined: Feb 2003
Posts: 939
F
frenchelectrican Offline
Member
Normally I use the ballast data to sized the circuit and I don't bother to read the lamp wattage but useally resvered for ballpark figures plus add about 20% or so so you should land right on the spot.

Merci,
Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Re: Fluorescent Lighting calculations [Re: Obsaleet] #208108 12/27/12 06:33 AM
Joined: Oct 2000
Posts: 2,721
Scott35 Online Happy
Broom Pusher and
Member
I agree with the previously posts - use the Ballast Data.

BTW, A Magnetic Rapid Start Ballast Load for Driving (2) F40T12 Lamps would be:

Line Input - 120 VAC:
Line Amperes = 0.69A
ANSI Watts = 82W
Average Ballast Factor = 0.84
BEF (Eff. Factor) = 1.02

Line Input - 277 VAC:
Line Amperes = 0.33A
ANSI Watts = 90W
Average Ballast Factor = 0.87
BEF (Eff. Factor) = 1.04

BTW, these figures are for F40T12 Lamps driven with the Cathodes being constantly Heated - AKA Rapid Start / Hot Cathode Operation.
Values will be lower for Instant Start Ballasting.
For Programmed Start Ballasting, the initial or Maximum Values will be similar.

Lamps will almost always draw less Wattage than they are rated at - especially when operated in extremely Cold or Warm environments.

--Scott (EE)


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 8
NORCAL 3
Popular Topics(Views)
269,932 Are you busy
204,359 Re: Forum
192,577 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3