#207410 10/26/12 06:36 PM
Joined: Oct 2002
Posts: 830
S
Member
I got a customer who wants a service to supply a motor home and his utility building. The utility building is 12x16. Right now there is no outlets or light in the utiltiy bldg. He also wants to have an outlet he can plug his motor home into. My thought is to mount a 100 amp service on the utilty bldg. with outlets with in use covers for his motor home. Install at least one light and one outlet in the utility bldg. with the outlet on a GFCI. Is there anything in code that limits the size of the bldg. that a service is to be mounted too? I myself cannot think of any now. The bldg. is permanent but of course the motor home is not. The motor home has a 120 volt cord on it. Anything wrong with my idea here. I've never had to install a service on a bulding this small, but I don't think there is any violations just so it is at least 100 amps.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2007
Posts: 1,335
S
Member
Unless, the local jha has issue with it, I think you are good. Don't forget a second ground rod if no other grounding source is available. Also watch your overhead clearances if its going to be a service drop instead of a lateral


"Live Awesome!" - Kevin Carosa
Joined: Oct 2002
Posts: 830
S
Member
Thanks for the reply. Yes, I'll do the 2nd ground rod and it will be an underground service. Steve..

Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
This was a common installation here when they were still making trailer parks. The user got a block house instead of just a power post so they had a place to store their stuff that they did not take home every summer and the power there served the RV. There may be a real bathroom in the block house too.


Greg Fretwell
Joined: Feb 2002
Posts: 2,233
H
Member
You also might have to check with the zoning officer because some towns will not allow a second service on an out building. It can allow for a rental or business running out of the second building.

Joined: Oct 2002
Posts: 830
S
Member
I checked with the AHJ here and they said it was alright, but to make sure the motor home outlet was just for charging the motor home and not for permanent dwelling. They said the meter could be pulled if it were a permanent dwelling. Don't know exactly how they would determine this, but the homeowner did say it was for temporary use.

Last edited by sparkync; 10/29/12 07:31 PM.
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
If it was a permanent building and you only served it with a single 120v circuit, the requirements are minimal anyway.


Greg Fretwell
Joined: Jul 2007
Posts: 1,335
S
Member
Probably a zoning issue. if the RV was going to be a permanent fixture, then it would need to hard wired