If they want you to "Certify" wiring in a house you might be able to write a letter such as,
On this date, I did a NON destructive inspection of the wiring in your house, and judging by what I could see, the wiring in the house seems to meet the present electrical code. CSA has a standard for inspecting existing homes so I just write "inspected to CSA standard..." It's a good system because it takes into consideration that a home might have met code a few years ago and the wiring is still safe.
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
Harold: I have to take exception to your words.... "On this date, I did a NON destructive inspection of the wiring in your house, and judging by what I could see, the wiring in the house seems to meet the present electrical code."
As the majority of the resi resales are 'older' homes, if I was writing this letter, it would say...'appears to be visually compliant with the NEC that was in effect when it was built' Additionally, if any work was performed, that should be listed ie: GFI receptacles installed at kitchen countertop, first floor powder room, etc.
John
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
TWH:
Could you post a link to that CSA standard if it is available on the web?
That sounds like a great idea.
John
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
Sparkyak:
"The point of hiring a professional is to deal with an issue."
IMHO, the discussion regarding the "Home Inspectors" falls into a scenario like this:
Here in NJ: Most (if no all) of the HI reports that I have seen consist of many pages of comments, and observations from roof condition to the dripping basement faucet. There is a 'disclaimer' that alludes that a Licensed Electrical Contractor' be consulted/retained to perform a thorough electrical system inspection.
The 'report' regarding the electrical from the average HI is something like..."dangerous FPE panel must be replaced"; "no receptacle outlet at xxx"; "non-operative GFI recept at xxx", "kitchen recepts not spaced to NEC", etc.
John
|
|
|
|
Joined: Jul 2007
Posts: 1,335
Member
|
I understand what you are saying. If you can't professionally do it your self, bring in an expert. I've seen good and bad home inspections. Anyone can disclaim their whole job away. I put disclaimers in my electrical inspections. At the same time, I wouldnt dive into home inspections be cause my lack of expertise.
What I'm saying is if an HI is not doing an electrical rather him/herself or bringing in a sub, they are not doing the job they were hired to do. A non professional hires pros to deal with the headaches of a job
"Live Awesome!" - Kevin Carosa
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
John
|
|
|
|
Joined: Mar 2004
Posts: 947
Member
|
TWH: Could you post a link to that CSA standard if it is available on the web? That sounds like a great idea. http://shop.csa.ca/en/canada/c221-canadian-electrical-code/cancsa-c226-no-1-11/invt/27032262011/It's advertised as $126 for 78 pages, but I'm reluctant to recommend it. My pdf reader shows 70 pages including the cover, blank pages and a page about how it contains recycled material. It might have been much more concise. The good part is that it covers the basics like height of overhead lines, loose and damaged fittings, and connecting aluminum wire to non-aluminum devices using pigtails, etc.
|
|
|
|
Joined: Feb 2002
Posts: 2,233
Member
|
In one of my towns there is one EC who loves to go in and "Certify" jobs. It usually costs the HO more than if he did the job from the start. Most EC's I know don't want to to certify anything that they didn't do.
|
|
|
Tom
Shinnston, WV USA
Posts: 1,044
Joined: January 2001
|
|
|
|