Hello, I am not familiar with AFCI because I strictl do Comm and Ind. I did the electrical work on my brother n law's house addition and ran 14/3 to feed receptacles in two new rooms. Two single pole AFCI (SquareD) breakers are not working. It will trip as soon as any load is applied to receptacle. Obviously because neutral is shared. I have read conflicting things on another site. One person states you can use a 2pole AFCI for multi branch circuits. Anothr said Square D doesnt make two pole, and another siad you CAN use two single pole. Can I run a white wire in between the single pole breakers? Any help would be great!

Horizontal Ad
Joined: Jun 2004
Posts: 1,273
T
Member
Run 14/2/2 -- AFCI demands dedicated neutrals for its logic. Period.


Tesla
Joined: Jul 2004
Posts: 10,024
Likes: 37
G
Member
You can't use a pair of single pole AFCIs. There may be a 2 pole AFCI that will handle a multiwire circuit but I haven't seen one.
The AFCI has pretty much made the residential multi wire circuit a thing of the past. Using more copper is probably cheaper than the 2 pole AFCI to serve it.
(or so Schnider says)

http://static.schneider-electric.us...t%20Interrupters-AFCI/0760DB0203R902.pdf

Cuttler Hammer may have a "classified" AFCI breaker that is listed to fit in a SqD panel. I will not start that argument here wink


Greg Fretwell
Joined: Dec 2001
Posts: 200
A
ayrton Offline OP
Member
Ok, well the house is closed up and painted. What would you suggest I do? I have a 14/3 run to the second floor, where 14/2 goes to one room, than 14/2 to another. How can I make these AFCI. I assume the inspector will come in with a AFCI tester to plug into random receptacles?

If I am remembering correctly (this was late spring when it was roughed) I put a j box in the attic and ran the 14/3 homerun to it than split off to 14/2 to each room. I suppose I can eliminate the red on the multi wire and just use one circuit for all. I hate to do it, but if the two pole AFCI breaker will not support the single neutral I dont have a choice.

Last edited by ayrton; 08/16/12 01:26 PM.
Joined: Jul 2004
Posts: 10,024
Likes: 37
G
Member
If you can't find an acceptable C/H classified breaker for your panel I think you are in trouble.
Make sure you get the listing documentation for the breaker and I think they come with a sticker for the panel.

YMMV as to how your AHJ feels about classified breakers.
It is probably worth a call before you shell out the $40-50 for the breaker.


Greg Fretwell
Joined: Dec 2001
Posts: 200
A
ayrton Offline OP
Member
Originally Posted by gfretwell
If you can't find an acceptable C/H classified breaker for your panel I think you are in trouble.
Make sure you get the listing documentation for the breaker and I think they come with a sticker for the panel.

YMMV as to how your AHJ feels about classified breakers.
It is probably worth a call before you shell out the $40-50 for the breaker.


I am a little confused? C/H...Cutler Hammer? From what the other fellow said nothing I do will work with a multi branch. If you see what I wrote at the bottom of my last post, I think that is the only solution.

Joined: Jul 2004
Posts: 10,024
Likes: 37
G
Member
I believe CH does have a 2 pole AFCI breaker that would work with a MW circuit. The question is whether it will work in your panel. Is this Homeline or QO?





Greg Fretwell
Horizontal Ad
Joined: Dec 2001
Posts: 200
A
ayrton Offline OP
Member
QO

Joined: Jul 2004
Posts: 10,024
Likes: 37
G
Member
I put the question in to C/H. Let's see what they say.


Greg Fretwell
Joined: Dec 2001
Posts: 200
A
ayrton Offline OP
Member
Originally Posted by gfretwell
I put the question in to C/H. Let's see what they say.


Ok thanks. I put in a call to Eaton and left message. I also contacted customer support via email

Page 1 of 3 1 2 3

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 812
Joined: April 2004
Top Posters(30 Days)
Trumpy 5
davey 1
Popular Topics(Views)
550,191 Are you busy
424,824 Re: Forum
396,158 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5