csst bonding #206357
06/18/12 11:08 PM
06/18/12 11:08 PM
S
schenimann  Offline OP
Member
Joined: Feb 2008
Posts: 193
Western North Carolina
Property management called about a gas leak in the csst piping. there was no bonding and lighting punctuured a hole in the pipe. Now they want it bonded. It is a pool house feeding a boiler for the pool heater. Does my #6 need to go back to the service in the main building or can I take it to the 200amp sub in the basement? I don't know if the sub panel has a ground rod. Thanks.

Work Gear for Electricians and the Trades
Re: csst bonding [Re: schenimann] #206358
06/18/12 11:48 PM
06/18/12 11:48 PM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
Corrugated Stainless Steel Tubing ( CSST ) plainly functions like a CHOKE during lightning events.

Hence, one should give it the full GEC bonding treatment...

With bushings at every choke point.

Corona discharge is prone to punch through at sharp turns - right through the PVC skin. So, every attempt should be made to not have them.

I'd take my bonding run as far back as necessary to assure that I've got an equipotential plane.



Tesla
Re: csst bonding [Re: schenimann] #206399
06/28/12 11:03 PM
06/28/12 11:03 PM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Here in NJ you have to take a ground clamp on the customer side of the gas pipe back to the grounding electrode of the electrical service. That means to me, you can connect to the #4 cu wire at the ground rod, or hit the inter-system grounding point of the electrical service. I believe there are a few more options, but these are the easiest to follow.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,370 Are you busy
187,982 Re: Forum
177,527 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 15 (0.005s) Memory: 0.9511 MB (Peak: 1.0765 MB) Zlib enabled. Server Time: 2018-10-18 05:04:32 UTC