type NM in conduit #206304
06/15/12 11:27 AM
06/15/12 11:27 AM
J
jkraft  Offline OP
Member
Joined: May 2003
Posts: 74
Hello,
Can someone direct me to the NEC section regarding sleeveing romex in conduit for a combination of 12/2 and 14/2, over 10'
thanks,
Joe

2017 / 2014 NEC & Related Books and Study Guides
Re: type NM in conduit [Re: jkraft] #206307
06/15/12 12:14 PM
06/15/12 12:14 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,222
Estero,Fl,usa
334.15(B)
Quote
Protection from Physical Damage. Cable shall be protected from physical damage where necessary by rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, or other approved means. Where passing through a floor, the cable shall be enclosed in rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, or other approved means extending at least 150 mm (6 in.) above the floor.


Note 9 to table 9 (conduit fill) says
Quote
(9)A multiconductor cable or flexible cord of two or more conductors shall be treated as a single conductor for calculating percentage conduit fill area. For cables that have elliptical cross sections, the cross-sectional area calculation shall be based on using the major diameter of the ellipse as a circle diameter.


two cables can't be stacked and measured, You have to compute for "2 conductors" the size of the widest dimension so you end up with some pretty big pipe.
I haven't run the numbers on a 12 and a 14 but 1" would not surprise me


Greg Fretwell
Re: type NM in conduit [Re: gfretwell] #206308
06/15/12 12:41 PM
06/15/12 12:41 PM
J
jkraft  Offline OP
Member
Joined: May 2003
Posts: 74
thanks for your help Greg, looking at those sections now and trying to determine what size IMC would be needed for 1-12/2 and 2-14/2???

Re: type NM in conduit [Re: jkraft] #206309
06/15/12 02:03 PM
06/15/12 02:03 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,222
Estero,Fl,usa
OK lets run the numbers
I will use commie metric because I prefer decimals

The 14ga I have measures 9mm, 12ga measures 10mm (across the widest part.

The area is the radius (half the diameter above)squared times pi (3.14)

5 x 5 x 3.14 = 78.5 mm2
4.5 x 4.5 x 3.14 = 63.6 mm2
Total cable area = 142.1 mm2

Take that to table 9 IMC "2 wire" column and you end up with 1" IMC (up to 192 mm2)
3/4 only gives you 117 mm2

See why I wasn't surprised? wink



Greg Fretwell
Re: type NM in conduit [Re: jkraft] #206316
06/15/12 09:59 PM
06/15/12 09:59 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Nice answer Greg. Not everyone knows about this approach. Most contractors want to skin the outer jacket from the NM cable and not worry about the rules. A clear violation of 312.5(C)(e).

Last edited by George Little; 06/15/12 10:12 PM.

George Little
Re: type NM in conduit [Re: jkraft] #206317
06/15/12 11:27 PM
06/15/12 11:27 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,963
Brick, NJ USA
Greg:
Ditto with what George said! Nice!!


John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sbi
sbi
indiana
Posts: 47
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
twh 12
Popular Topics(Views)
246,848 Are you busy
184,205 Re: Forum
173,446 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 15 (0.003s) Memory: 0.9770 MB (Peak: 1.1263 MB) Zlib enabled. Server Time: 2018-05-21 03:03:36 UTC