Brief buzzing from breaker #204397
12/07/11 02:41 AM
12/07/11 02:41 AM
H
Hemingray  Offline OP
Member
Joined: Apr 2005
Posts: 199
Lehigh Acres, FL
Have an interesting issue here:

Turning on the outside christmas lights (I have alot of them), the 20A breaker for the circuit that some of them are on, buzzes briefly before quieting down. Circuit in question is a dedicated 20A line for this purpose, one of two installed. The other one does not buzz. Perhaps a worn breaker needing replacement soon?


Cliff
Work Gear for Electricians and the Trades
Re: Brief buzzing from breaker [Re: Hemingray] #204398
12/07/11 03:39 AM
12/07/11 03:39 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,298
Estero,Fl,usa
Put a clamp on it and see what you are pulling. This is probably telling you that you have exceeded the 16a continuous load you are allowed.


Greg Fretwell
Re: Brief buzzing from breaker [Re: Hemingray] #204402
12/07/11 10:39 AM
12/07/11 10:39 AM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Does the breaker feel warm? That could also be from a lose connection.

Re: Brief buzzing from breaker [Re: Hemingray] #204404
12/07/11 12:44 PM
12/07/11 12:44 PM
T
twh  Offline
Member
Joined: Mar 2004
Posts: 947
Regina, Sask.
Some breakers buzz and some transformers and ballasts buzz. Replace them when the annoyance factor makes the cost worthwhile.

Re: Brief buzzing from breaker [Re: Hemingray] #204445
12/10/11 12:06 AM
12/10/11 12:06 AM
H
Hemingray  Offline OP
Member
Joined: Apr 2005
Posts: 199
Lehigh Acres, FL
It's stopped doing it at this point.


Cliff
Re: Brief buzzing from breaker [Re: Hemingray] #204450
12/10/11 04:24 AM
12/10/11 04:24 AM
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
I have heard Buzzing emitted from correctly installed and functioning MCCBs.
Always figured the sound is Generated from the Spring in the Reset Assembly.

Would be nice to know exactly which entity is vibrating, and what factors determine it to be Audible.

-- Scott


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Re: Brief buzzing from breaker [Re: Hemingray] #204475
12/12/11 10:32 AM
12/12/11 10:32 AM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Isn't there usually a lot of buzz around Christmas time?



Sorry for that bad joke! I just had to say it. smile


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,903
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,393 Are you busy
188,004 Re: Forum
177,570 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.027s Queries: 15 (0.005s) Memory: 0.9857 MB (Peak: 1.1426 MB) Zlib enabled. Server Time: 2018-10-18 20:40:36 UTC