Staircase Pressurization Fan Motor Overload #203328
09/22/11 02:41 AM
09/22/11 02:41 AM
S
sccat  Offline OP
Member
Joined: Jun 2005
Posts: 14
CHN
Is there a Thermal Relay in a DOL starter for "staircase pressurization fan"?
When motor overload happens,will the Thermal Relay cut off the contactor?

Work Gear for Electricians and the Trades
Re: Staircase Pressurization Fan Motor Overload [Re: sccat] #203336
09/22/11 05:55 PM
09/22/11 05:55 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,997
Brick, NJ USA
Your second question: Thermal OLs 'open', and the motor starter opens (Off).

First question may require more than the NEC, as staircase pressurization is Building & Fire Safety Codes. I suggest that you contact the local AHJs in whatever area you are working in. My opinion would be no OLs, just short circuit protection as this is a life safety item, perhaps like a fire pump. Just my opinion.



John
Staircase Pressurization Fan Motor Overload #203396
09/27/11 12:57 AM
09/27/11 12:57 AM
S
sccat  Offline OP
Member
Joined: Jun 2005
Posts: 14
CHN
Is there a Thermal Relay in a DOL starter for "staircase pressurization fan"?
When motor overload happens,will the Thermal Relay cut off the contactor?

Re: Staircase Pressurization Fan Motor Overload [Re: sccat] #203397
09/27/11 01:20 AM
09/27/11 01:20 AM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
Only ONCE did I have to build such a circuit.

The AHJ determined that such a blower is NOT a life essential device.

So the OL heaters were left in place.

-----

Each situation is going to be a Life Safety issue. It's outside the NEC.

----

WRT smaller ( 1hp or less ) thermal overloads lead directly to integral drop-out from the load.

Not uncommonly, they reset, automatically, when the temp drops they re-trigger. They DO NOT interact with any contactor what so ever.

These beasties interrupt line current -- and then restore it.

These motors are so small that contactors are uncommon.



Tesla
Re: Staircase Pressurization Fan Motor Overload [Re: sccat] #203402
09/27/11 06:45 AM
09/27/11 06:45 AM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,236
SI,New Zealand
Originally Posted by sccat
Is there a Thermal Relay in a DOL starter for "staircase pressurization fan"?
When motor overload happens,will the Thermal Relay cut off the contactor?


In a Direct On Line starter, your only real protection is thermal via the overloads at the base of the contactor.
This should by rights open the control circuit and shut everything off, unless it has been poorly designed or wired.

This is first year apprentice stuff, why do you ask?

Re: Staircase Pressurization Fan Motor Overload [Re: sccat] #203404
09/27/11 09:10 AM
09/27/11 09:10 AM
S
sccat  Offline OP
Member
Joined: Jun 2005
Posts: 14
CHN
Some people think that "staircase pressurization fan" is a Life Safety Equipment as "fire pump".

Re: Staircase Pressurization Fan Motor Overload [Re: sccat] #203406
09/27/11 09:34 AM
09/27/11 09:34 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,997
Brick, NJ USA
Sccat:

You have this posted in the NEC section from 9/22/2011, which has one response. I'll merge the two together.

You're right!! Now, it will depend on 'who' the 'some people' are!!

The best solution I would suggest is to speak to the local AHJ about this. IF the ventilation system is considered 'life safety' or not.

Last edited by HotLine1; 09/27/11 09:36 AM. Reason: prep to merge

John
Re: Staircase Pressurization Fan Motor Overload [Re: sccat] #203408
09/27/11 11:51 AM
09/27/11 11:51 AM
S
sccat  Offline OP
Member
Joined: Jun 2005
Posts: 14
CHN
NFPA 92A-2006 Standard for Smoke-Control Systems Utilizing Barriers and Pressure Differences

Annex D Fire Fighters’ Smoke-Control Station Considerations

Control actions issued from the FSCS should not override or bypass devices and controls intended to protect against electrical overloads, provide for personnel safety, and prevent major system damage.

Is "Staircase Pressurization Fan " a part of "Smoke-Control Systems"?

Re: Staircase Pressurization Fan Motor Overload [Re: sccat] #203409
09/27/11 02:58 PM
09/27/11 02:58 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,997
Brick, NJ USA
Again, I say...talk to the local AHJ!

BTW, you profile states your location as "CHN", would you care to elaborate on that please?



John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,895
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
248,604 Are you busy
186,340 Re: Forum
175,796 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.034s Queries: 15 (0.005s) Memory: 1.0042 MB (Peak: 1.1742 MB) Zlib enabled. Server Time: 2018-08-18 12:15:05 UTC