PV inverter output #203349 09/23/11 04:47 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline OP
Member
A student asked me a question about the inverter output that I could not answer to my own satisfaction.

Why does the PV inverter (connected to the service panel) feed loads inside the building first then send excess power out into the grid?

Or, to put it another way, how does this dinky little 3 kw inverter push power out into the grid working against all those megawatts?

I could take a S.W.A.G. on this & I might even get it right, but I would like to know for sure.

Tom


Few things are harder to put up with than the annoyance of a good example.
Tools for Electricians:
Re: PV inverter output [Re: Tom] #203350 09/23/11 05:07 PM
Joined: Jul 2004
Posts: 9,546
G
gfretwell Offline
Member
My guess, it is just a slightly higher voltage so it isn't pushing against anything.


Greg Fretwell
Re: PV inverter output [Re: Tom] #203351 09/23/11 06:20 PM
Joined: May 2011
Posts: 10
A
AdrianW Offline
Member
Alas, with synchronised AC systems it just isn't that simple! (as it would be with DC) Just having a higher voltage would cause the inverter to export reactive power (VAr) but not real power (kW). To export real power it must create a sinewave which is very slighly ahead of the sinewave from the grid....ie its trying to pull the grid faster, this causes it to export power.

Adrian

Re: PV inverter output [Re: Tom] #203354 09/23/11 09:53 PM
Joined: Jul 2004
Posts: 9,546
G
gfretwell Offline
Member
Yes but if it peaked at the same time, it would be ahead of the grid.


Greg Fretwell
Re: PV inverter output [Re: gfretwell] #203358 09/24/11 05:23 AM
Joined: May 2011
Posts: 10
A
AdrianW Offline
Member
No, it wouldn't. If it peaked at the same time it would be in-phase with the grid - there would be no phase angle difference & no power would transfer. Even if the magnitude of the sinewave were bigger it would still only export reactive power.

The inverter sinewave must be a few degress ahead of the grid sinewave & attempting to "pull it faster" in order to export real power.

Think about generator theory. Remember that when a generator is operating in parallel with the grid controlling excitation influences reactive power & the torque from the prime mover determines the real power - the prime mover is trying to pull the generator rotor out-of-step with the magnetic field created in the stator by the grid. This ripping apart of the two magnetic fields is what causes the generation of real power. A similar process has to happen with the inverter.

Adrian

Re: PV inverter output [Re: Tom] #203366 09/25/11 01:55 AM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
Adrian...

Nope.

Only voltage superiority injects power.

The frequency can't be tampered with -- such would create crazy harmonics.

The inverter sends power to the system by staying entirely in synch...

But at a trivially higher voltage. That's all it takes.

Because of voltage drop over distance -- the local loads will 'feel' the PV first.

Only after they are saturated by the PV array will enough 'over-voltage' remain for energy ( joules ; watt-seconds ) ever make it out into the grid.

Leading the Poco's frequency absolutely DOES NOT WORK. Instead, you would impose a harmonic upon the grid...

Something that would draw finger wags from the Poco.


Tesla
Re: PV inverter output [Re: Tom] #203375 09/25/11 03:28 PM
Joined: May 2011
Posts: 10
A
AdrianW Offline
Member
No, sorry I can't agree.

For a synchronised AC system, changing the voltage can only ever change the REACTIVE power exported. It cannot influence the REAL POWER.

Your ideas would work with a DC system - but the grid is not DC. Life in the AC world is far more complicated than just offering a higher higher voltage.

Adrian

Re: PV inverter output [Re: Tom] #203376 09/25/11 03:49 PM
Joined: Jul 2004
Posts: 9,546
G
gfretwell Offline
Member
I am still not sure how you can say that a 100% in phase level that is higher does not lead the lower signal.

If you look at this picture you clearly see the higher voltage is there earlier and leaves later.

[Linked Image from gfretwell.com]


Greg Fretwell
Re: PV inverter output [Re: Tom] #203377 09/25/11 04:59 PM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
Greg...

That's a beautiful snapshot off a scope.

It illustrates that the inverter is ALWAYS beyond the voltage of the Poco -- if it is to drive energy back up the line.

Frequency deviations simply do NOT work.


Tesla
Re: PV inverter output [Re: Tesla] #203388 09/26/11 03:36 PM
Joined: Jul 2004
Posts: 783
L
LarryC Offline
Member
Gentlemen,

I believe in a paralleled generator situation like Adrian is talking about, he is correct.

When synchronizing generators to the grid, you increase the speed control to take on more real load. The actual generator speed does not change because it is locked to the grid frequency due to the circulating currents, however it will pick up more of the real power load.

To increase the paralled generator's reactive loading, you try to increase the generator's output terminal voltage.

I believe the grid tie inverters are designed to try to vary their output frequency to control how much real power they output. Obviously a KW sized unit will not pull the utility units off frequency, but they will try to unload them.

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,184 Are you busy
206,070 Re: Forum
194,081 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3