AE-Gifts, Affordable Everyday
0 members (), 191 guests, and 13 robots.
Page 3 of 3 1 2 3
I was going to bring that up myself wink
It can be ordered either way tho.
The wiring on the load side of the service point has always had a full sized neutral in my experience.
I never gave much thought to what the PoCo was doing since I didn't have much ability to change it.
Greg:
Yes, triplex is reduced, but that is on their side!
My references are to typical NJ (PSE&G) secondaries that are 'customer installed' from pad mount xfrs. The rule also applies to O/H.
I agree, everything on "my side" has had full sized neutrals.
God willing, and the creek don't rise (again!) I'll be installing 11 runs of 750KCMIL w/ 250 KCmil grounds monday
at first sniff that 250 seemed a tad small
but they're not calling it a neutral
they're calling it a groundING conductor (there's your 12.5%)
and 'earthing' a noodle from the 4000A 480 switchgear
this was engineered , and done so with both the poco and architectual engineers working in unision btw
all code ref's aside, i just don't like creating something that is readilly available, especially in close proximty to so many potential returns to the serving xfomer (or the other 2000A xfomer bank aboput 40' away)
~S~
Page 3 of 3 1 2 3
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
dsk 1
561,583 Are you busy
435,235 Re: Forum
404,033 Need opinion
