#202429 08/03/11 01:27 PM
Joined: Feb 2002
Posts: 2,233
H
Member
Did we have the conversation before or not. I can't remember, there have been so many topics covered here.

If you place a hot tub/spa outside on a wooden deck and the deck is up in the air off the ground. ( height doesn't matter) What do you do with the equipotential bonding grid? (EBG) Do you run it around the tub under the deck? Or leave it out completely? Or what?

Work Gear for Electricians and the Trades

Workgear for Electricians

harold endean #202432 08/03/11 02:10 PM
Joined: Jul 2004
Posts: 10,042
Likes: 37
G
Member
If you read the letter of the code, you still need to bond the dirt under the deck or if you read it the other way you have to bond the wood. Non-conducting decking is really not addressed, nor is it excepted.

I think CMP 17 has been snorting the HTH.


Greg Fretwell
harold endean #202433 08/03/11 02:53 PM
Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
Harold:

This is a tough one IMHO. Conflicting 'he said/she said', and a gray area within the NEC.

There are differing opinions on the conductivity of wood, which I don't want to debate, although someone will. Composite decking is also a debate by some.

Opinions that I have heard range from the absurd (IMHO) of 'bonding the wood' to ....nothing.

Most spas that I have seen install the rubber type listed mats under and around the spa; case closed.

Installs on existing concrete or paver patios are another tough call. Bonding the existing rebar/mesh is one option, the pads is another, or the grid around the slab. Problems arise when the 'slab' is a large patio. Solutions range from finding the rebar/mesh to saw cuts & #8, or..the pads.

Welcome to confusion!!


John
harold endean #202435 08/03/11 03:54 PM
Joined: Jan 2005
Posts: 5,485
Likes: 4
Cat Servant
Member
Now try to explain this statement to Joe Handyman:

"We'll laugh ourselves silly when we find you ran a GEC to the incoming plastic water line, but we'll red-tag you if you fail to bond the plastic deck."

harold endean #202437 08/03/11 04:31 PM
Joined: Jul 2004
Posts: 10,042
Likes: 37
G
Member
Has anyone written a proposal yet?


Greg Fretwell
gfretwell #202449 08/04/11 08:03 AM
Joined: Oct 2000
Posts: 5,393
S
Member
apparently the CMP's insist on one shoe fitting all

for instance , would you feel comfortable installing a grounding grid under a spa that is in proximity to the service entrance g'ding electrodes?

~S~

harold endean #202457 08/04/11 02:01 PM
Joined: Jul 2004
Posts: 10,042
Likes: 37
G
Member
Why not? The pool/spa ground grid is going to be bonded to the EGC of the supply conductors in a number of places and that is bonded to the GEC.
In the case of a gunite in ground pool, that is ultimately you best grounding electrode, even though we are slow to admit it.
If it is concrete or metal at my house, it is bonded.


Greg Fretwell
Work Gear for Electricians and the Trades

Workgear for Electricians

gfretwell #202480 08/04/11 10:04 PM
Joined: Oct 2000
Posts: 5,393
S
Member
Originally Posted by gfretwell
Why not? The pool/spa ground grid is going to be bonded to the EGC of the supply conductors in a number of places and that is bonded to the GEC.
In the case of a gunite in ground pool, that is ultimately you best grounding electrode, even though we are slow to admit it.
If it is concrete or metal at my house, it is bonded.



well my point is , it's a potential noodle Greg

i mean, the more we bond, ground, lightning 780, or EGC a place, the more noodle potential it will have....~S~

Last edited by sparky; 08/04/11 10:05 PM. Reason: no glasses, dammit!
harold endean #202486 08/04/11 10:42 PM
Joined: Jul 2004
Posts: 10,042
Likes: 37
G
Member
Noodle?


Greg Fretwell
harold endean #202488 08/04/11 10:48 PM
Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
Greg:

That's a common term in some areas for 'neutral'.


John