Wiring Methods #202281 07/29/11 03:57 PM
Joined: May 2010
Posts: 30
B
Bravo Offline OP
Member
Is it legal or feasible to use a conduit body to transition from electrical metallic tubing (EMT) to type SOOW power cord with a fitting that joins these two raceways instead of installing a box?

Above hung ceiling will be EMT, Below will be the Pwr Coord. The conduit will be used to splice 3#6AWG & 1#10AWG wire.

Thanks in advance.


2017 / 2014 NEC & Related Books and Study Guides
Re: Wiring Methods [Re: Bravo] #202282 07/29/11 04:30 PM
Joined: Apr 2002
Posts: 7,218
HotLine1 Offline
Member
IF you could locate a condulet that was identified for containing splices, and of sufficient size (CI) for the conductors....no problem.

Please keep in mind the sparky that will have to do this, IF you locate a compliant condulet.



John
Re: Wiring Methods [Re: HotLine1] #202283 07/29/11 04:33 PM
Joined: May 2010
Posts: 30
B
Bravo Offline OP
Member
How do I locate a compliant conduit body?

Re: Wiring Methods [Re: Bravo] #202285 07/29/11 04:44 PM
Joined: Apr 2002
Posts: 7,218
HotLine1 Offline
Member
That's not going to be easy.

There are condulets that are identified/listed as suitable for splicing, and those should be marked with CI capacity or quantity & size of conductors.

RedDot may be a mfg to start with, or a good counter guy at a real supply house.

Personally, I would go with a suitable box.



John
Re: Wiring Methods [Re: Bravo] #202288 07/29/11 10:39 PM
Joined: Jan 2004
Posts: 1,507
G
George Little Offline
Member
The code reference you are dealing with is Article 314 Section 314.16(C).


George Little
Re: Wiring Methods [Re: Bravo] #202291 07/29/11 11:45 PM
Joined: Apr 2002
Posts: 7,218
HotLine1 Offline
Member
A little further on this.

(C) Conduit Bodies.
(1) General. Conduit bodies enclosing 6 AWG conductors
or smaller, other than short-radius conduit bodies as described
in 314.16(C)(2), shall have a cross-sectional area
not less than twice the cross-sectional area of the largest
conduit or tubing to which they can be attached. The maximum
number of conductors permitted shall be the maximum
number permitted by Table 1 of Chapter 9 for the
conduit or tubing to which it is attached.
(2) With Splices, Taps, or Devices. Only those conduit
bodies that are durably and legibly marked by the manufacturer
with their volume shall be permitted to contain
splices, taps, or devices. The maximum number of conductors
shall be calculated in accordance with 314.16(B). Conduit
bodies shall be supported in a rigid and secure manner

314.16 (b) table requires 5 CI for each #6, & 2.5 CIfor the #10

Sounds like 38.5CI .

Using Red Dot mfg data, you will need a 2" LB/LL/LR for your conductors.

Last edited by HotLine1; 07/29/11 11:46 PM. Reason: typo

John
Re: Wiring Methods [Re: HotLine1] #202308 07/30/11 07:45 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
or......?

[Linked Image from garvinindustries.com]

Re: Wiring Methods [Re: Bravo] #202313 07/30/11 08:16 PM
Joined: Apr 2002
Posts: 7,218
HotLine1 Offline
Member
sparky:

I really had a thought about the above, but I wanted to stay serious.



John
Re: Wiring Methods [Re: Bravo] #202318 07/31/11 12:23 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Just how far is it from your last box?

I see no problem with using a simple connector/coupling/cord grip assembly on the end of the pipe, with the cord running in the pipe all the way back to the box- thus not needing a splice at the transition.

Re: Wiring Methods [Re: Bravo] #202321 07/31/11 01:05 PM
Joined: Jul 2004
Posts: 9,547
G
gfretwell Offline
Member
"Cord in a raceway" would raise an eyebrow in a lot of places.
It is not a chapter 3 wiring method.


Greg Fretwell
Page 1 of 4 1 2 3 4

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,205 Are you busy
206,090 Re: Forum
194,093 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3