Is it legal or feasible to use a conduit body to transition from electrical metallic tubing (EMT) to type SOOW power cord with a fitting that joins these two raceways instead of installing a box?
Above hung ceiling will be EMT, Below will be the Pwr Coord. The conduit will be used to splice 3#6AWG & 1#10AWG wire.
Thanks in advance.
Posts: 7,413 Likes: 10
IF you could locate a condulet that was identified for containing splices, and of sufficient size (CI) for the conductors....no problem.
Please keep in mind the sparky that will have to do this, IF you locate a compliant condulet.
How do I locate a compliant conduit body?
That's not going to be easy.
There are condulets that are identified/listed as suitable for splicing, and those should be marked with CI capacity or quantity & size of conductors.
RedDot may be a mfg to start with, or a good counter guy at a real supply house.
Personally, I would go with a suitable box.
The code reference you are dealing with is Article 314 Section 314.16(C).
George Little
A little further on this.
(C) Conduit Bodies. (1) General. Conduit bodies enclosing 6 AWG conductors or smaller, other than short-radius conduit bodies as described in 314.16(C)(2), shall have a cross-sectional area not less than twice the cross-sectional area of the largest conduit or tubing to which they can be attached. The maximum number of conductors permitted shall be the maximum number permitted by Table 1 of Chapter 9 for the conduit or tubing to which it is attached. (2) With Splices, Taps, or Devices. Only those conduit bodies that are durably and legibly marked by the manufacturer with their volume shall be permitted to contain splices, taps, or devices. The maximum number of conductors shall be calculated in accordance with 314.16(B). Conduit bodies shall be supported in a rigid and secure manner
314.16 (b) table requires 5 CI for each #6, & 2.5 CIfor the #10
Sounds like 38.5CI .
Using Red Dot mfg data, you will need a 2" LB/LL/LR for your conductors.
or......? ![[Linked Image from garvinindustries.com]](http://www.garvinindustries.com/Images/MOLB-100.jpg)
sparky:
I really had a thought about the above, but I wanted to stay serious.
Posts: 5,485 Likes: 5
Just how far is it from your last box?
I see no problem with using a simple connector/coupling/cord grip assembly on the end of the pipe, with the cord running in the pipe all the way back to the box- thus not needing a splice at the transition.
Posts: 10,055 Likes: 40
"Cord in a raceway" would raise an eyebrow in a lot of places. It is not a chapter 3 wiring method.