electrical conduit sharing trench with gas #201852
06/28/11 03:45 PM
06/28/11 03:45 PM
Niko  Offline OP
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
Can the gas line share the same trench with the electrical conduit? They are both branch circuits and are not on the service side.

I know it is not an NEC issue.

Thank you.

Last edited by Niko; 06/28/11 03:46 PM.

Be kind to your neighbor, he knows where you live

Work Gear for Electricians and the Trades
Re: electrical conduit sharing trench with gas [Re: Niko] #201853
06/28/11 05:38 PM
06/28/11 05:38 PM
HotLine1  Online Content

Member
Joined: Apr 2002
Posts: 6,950
Brick, NJ USA
Niko:
Check locally IMHO.

Here in NJ it's not an issue as long as they are not 'side-by-side'.

You may have siesmic issues.


John
Re: electrical conduit sharing trench with gas [Re: Niko] #201868
06/29/11 12:40 AM
06/29/11 12:40 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,199
Estero,Fl,usa
I agree with John. Local policy will dictate this and it may actually be the utilities driving it.


Greg Fretwell
Re: electrical conduit sharing trench with gas [Re: Niko] #201870
06/29/11 12:48 AM
06/29/11 12:48 AM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
Pacific Gas & Electric does not permit it.

Underground natural gas delivery is by plastic.

No way will PG&E suffer compounding fires -- electric then gaseous.

Common trenches out my way are restricted to power, data, coax... with various horizons at least 12" apart -- sometimes more.

Fresh water, dark water, fire systems, and gas are not permitted in the common trench.

Customer side power is not permitted in the same horizon ( depth ) as utility lines. Utility power is always to be the deepest in the trench -- except if crossing.


Tesla
Re: electrical conduit sharing trench with gas [Re: Niko] #201872
06/29/11 01:23 AM
06/29/11 01:23 AM
Niko  Offline OP
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
Thanks guys.

I have emailed the plumbing inspector for advice.


Be kind to your neighbor, he knows where you live


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 222
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
245,928 Are you busy
182,996 Re: Forum
172,781 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.027s Queries: 15 (0.007s) Memory: 0.9684 MB (Peak: 1.1105 MB) Zlib enabled. Server Time: 2018-04-25 18:35:35 UTC