#201852 - 06/28/11 02:45 PM electrical conduit sharing trench with gas  
Niko  Offline
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
Can the gas line share the same trench with the electrical conduit? They are both branch circuits and are not on the service side.

I know it is not an NEC issue.

Thank you.

Last edited by Niko; 06/28/11 02:46 PM.

Be kind to your neighbor, he knows where you live


Work Gear for Electricians and the Trades

#201853 - 06/28/11 04:38 PM Re: electrical conduit sharing trench with gas [Re: Niko]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,878
Brick, NJ USA
Niko:
Check locally IMHO.

Here in NJ it's not an issue as long as they are not 'side-by-side'.

You may have siesmic issues.


John

#201868 - 06/28/11 11:40 PM Re: electrical conduit sharing trench with gas [Re: Niko]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,142
Estero,Fl,usa
I agree with John. Local policy will dictate this and it may actually be the utilities driving it.


Greg Fretwell

#201870 - 06/28/11 11:48 PM Re: electrical conduit sharing trench with gas [Re: Niko]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
Pacific Gas & Electric does not permit it.

Underground natural gas delivery is by plastic.

No way will PG&E suffer compounding fires -- electric then gaseous.

Common trenches out my way are restricted to power, data, coax... with various horizons at least 12" apart -- sometimes more.

Fresh water, dark water, fire systems, and gas are not permitted in the common trench.

Customer side power is not permitted in the same horizon ( depth ) as utility lines. Utility power is always to be the deepest in the trench -- except if crossing.


Tesla

#201872 - 06/29/11 12:23 AM Re: electrical conduit sharing trench with gas [Re: Niko]  
Niko  Offline
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
Thanks guys.

I have emailed the plumbing inspector for advice.


Be kind to your neighbor, he knows where you live



Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 15 (0.002s) Memory: 0.7699 MB (Peak: 0.9119 MB) Zlib enabled. Server Time: 2017-12-14 04:16:59 UTC