I was looking at the classified ads on this site. Somebody has a bunch of pole transformers that have 240/480 secondaries.

In what application would they be used?

Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
I see these around mine sites quite a bit. Many mine sites use 240 or 480 3 phase Delta ungrounded systems as permitted by 250.21 (A)(4). These transformers could also be used for a corner grounded Delta.


Few things are harder to put up with than the annoyance of a good example.
Joined: Jul 2004
Posts: 783
L
LarryC Offline OP
Member
OK, thanks.

Joined: Jul 2004
Posts: 783
L
LarryC Offline OP
Member
Is 240/480 delta a common configuration for oil fields too?

Joined: Feb 2004
Posts: 1,437
Member
yes it is... 99% of the 480V running around the oil fields in western Kern Co, CA are ungrounded delta sec's. with delta primary on 12KV systems and Wye on 21KV systems


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Top Posters(30 Days)
timmp 3
Popular Topics(Views)
282,926 Are you busy
216,694 Re: Forum
203,115 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5