Service Disconnect #200697
04/14/11 11:54 PM
04/14/11 11:54 PM
S
SJT  Offline OP
Member
Joined: Jul 2002
Posts: 241
PATCHOGUE, N.Y.
A Service Main disconnect could be outside the building or in the Bldg. right?
If the main is outside (near a transformer)then the first panel it feeds in the Bldg. would be a sub panel?
SJT

2017 / 2014 NEC & Related Books and Study Guides
Re: Service Disconnect [Re: SJT] #200700
04/15/11 02:09 AM
04/15/11 02:09 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,227
Estero,Fl,usa
Technically the service disconnect just has to be on the property but your AHJ may still want a disconnect on/in the building.
Yes that will become a feeder and you need to run the ECG along with a ground. As long as that is the feeder for the whole building, you can use 210.15(B)(6) in a dwelling. (Not commercial)

Last edited by gfretwell; 04/15/11 04:04 AM. Reason: Make the correction Niko pointed out

Greg Fretwell
Re: Service Disconnect [Re: SJT] #200701
04/15/11 03:36 AM
04/15/11 03:36 AM
Niko  Offline
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
Greg meant, 310.15(B)(6) for 2008 and 310.15(B)(7) for 2011


Be kind to your neighbor, he knows where you live

Re: Service Disconnect [Re: SJT] #200703
04/15/11 04:06 AM
04/15/11 04:06 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,227
Estero,Fl,usa
Thanks. I guess I should turn up the light when I type

I am not on the 2011, in protest of the CD thing wink


Greg Fretwell
Re: Service Disconnect [Re: SJT] #200714
04/16/11 12:00 AM
04/16/11 12:00 AM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,973
Brick, NJ USA
Be cautious on the location 'within the building'. Unprotected, unfused, conductors within a building, the distance allowed is not specific in the NEC. For the most part, it's left up to the local AHJ. I hear 12", 5', 3'4", but there is NO distance within the book & never was.

A main inside is accepted 'nearest to the point of entry', unless we use the 2" of concrete/brick exception. It all boils down to the AHJ's 'nearest' definition


John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 68
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
twh 5
Popular Topics(Views)
247,602 Are you busy
184,935 Re: Forum
174,161 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.029s Queries: 15 (0.005s) Memory: 0.9688 MB (Peak: 1.1099 MB) Zlib enabled. Server Time: 2018-06-20 00:06:08 UTC