ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
sec cable code conflict
by ghost307. 11/19/18 09:26 AM
This anti-theist is priceless!!!
by Texas_Ranger. 11/17/18 02:15 PM
High current GFI vs regular GFCI
by Texas_Ranger. 11/17/18 02:07 PM
Single phase and what you call it.
by dsk. 11/12/18 11:10 AM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 29 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Light Pole #200660
04/12/11 10:24 PM
04/12/11 10:24 PM
M
MJ2000  Offline OP
Member
Joined: Jun 2005
Posts: 17
Toronto, ON
Hi,
I have to replace two direct buried light poles with surface mount (10'x4").Where can I find specification for the pole foundation(how deep does the hole have to be )? Does the Inspector have to check it before I pour concrete on?

Thanks,

MJ

Tools for Electricians:
Re: Light Pole [Re: MJ2000] #200667
04/13/11 12:20 PM
04/13/11 12:20 PM
HotLine1  Online Content

Member
Joined: Apr 2002
Posts: 7,039
Brick, NJ USA
MJ:

Specs for the foundation is from the manufacturer of the pole. Or, (here in NJ) a Lic. PE is required.

I can tell you here a electrical insp is required for the trench/conduit and the pole base, along with any supplemental grounding (lightning) & bonding.

Our members in Canada will get back with CEC & provincial regs.....


John
Re: Light Pole [Re: MJ2000] #200670
04/13/11 03:25 PM
04/13/11 03:25 PM
G
ghost307  Online Content
Member
Joined: May 2005
Posts: 960
Chicago Illinois USA
You might have to ask a Strucural Engineer, depending on your circumstances.

The size and depth of the base is affected by the pole's height, how much stuff is on it (EPA=Effective Projected Area) and how windy it gets where you are.


Ghost307
Re: Light Pole [Re: MJ2000] #200672
04/13/11 05:52 PM
04/13/11 05:52 PM
M
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
Our Electrical installation department started buying and specing a precast base for all lamp and traffic standards.

For years we had used bolts and sonotubes with concrete but they take 28 days to reach full strength and often temporary traffic signals could be up for a month. Copper theft and other matters make this a poor choice.
I don't know what standard you are installing but the manufacturer should have a spec for the base and a bolt template for casting the foundation in place. Our stock bases are about 6 feet tall and shaped like a 4 sided pyramid. 4 feet across at the base and 1 foot across at the bolts.

Inspection rules fall under section 2 of the CEC and in provincial regulations which can vary from province to province. In BC it is the Safety Standards Act and the Electrical Safety Regulation that are the primary legislation governing electrical work.

These provincial acts can be found on the BCSA website.

In general an inspection is required for each phase of a job and before anything can be concealed whether by dirt or drywall.

A telephone pole has a 12 foot gain mark and depending on the length you must bury 1 meter plus %10 of the length of the pole. We use the gain mark to measure to ground level and subtract the above surface gain from 12 feet to determine if you buried the pole deep enough. Most pole contractors know this very well.

Last edited by mikesh; 04/13/11 05:56 PM.
Re: Light Pole [Re: MJ2000] #200685
04/14/11 12:30 AM
04/14/11 12:30 AM
M
MJ2000  Offline OP
Member
Joined: Jun 2005
Posts: 17
Toronto, ON
Thanks for the suggestions,

The existing pole was three feet buried in the 12" sonotube.
The pole is between the houses(wind isn't an issue) with vertical load(50lb). I will ask for a manufacturer spec, they should provide it.

MJ


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
Popular Topics(Views)
251,604 Are you busy
188,744 Re: Forum
178,454 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 15 (0.005s) Memory: 0.9692 MB (Peak: 1.1088 MB) Zlib enabled. Server Time: 2018-11-19 16:18:08 UTC