MAH #200180 03/23/11 11:17 PM
Joined: Mar 2011
Posts: 28
Member
I would say that GFCI just filters current. So Line from panel to the load to the shared neutral. What happ when power travels from opposite side. Unbalanced load flows only behind GFCI. If in CEC doesn't say it clearly, well you can and can't. That right inspectors reserve for themselfs.
If you don't see something a lot in practice people are sceptical about it. GFCI should be checked every month. Not for use everywhere.
In parrallel circuits:

voltage=constant
current=variable

If you split neutral before comming to GFCI you just changed current...

...or I am just talking nonsense


“If you don't know where you are going, any road will get you there”.
Horizontal Ad
MAH #200188 03/24/11 08:40 AM
Joined: May 2005
Posts: 984
Likes: 1
G
Member
A GFCI doesn't filter anything. It measures the current leaving the device on the phase wire (black) and the current returning to the device on the neutral wire (white) and then compares the two. In normal operation they should always be the same since electricity flows in a closed circuit.

If the two current measurements differ by more than a prescribed maximum amount (4-6 milliamperes), a contact inside the GFCI opens and shuts off the current flow.
So if 9 amperes is traveling through the heating elements in the toaster and 1 ampere is flowing up your arm, through your heart, down your other arm and into the faucet on the kitchen sink, that 1 ampere (1,000 milliampere) difference sensed by the GFCI will open the circuit at the device rather than stand there cooking yourself to death.


Ghost307
Page 2 of 2 1 2

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
timmp
timmp
Leo, IN, USA
Posts: 34
Joined: June 2004
Top Posters(30 Days)
BigB 4
Jam85 4
Popular Topics(Views)
328,004 Are you busy
252,854 Re: Forum
235,486 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5