Joined: Nov 2002
Posts: 12
K
kitha Offline OP
Member
I have the service entrance panel in one building(say bldg#1) and it feeds to an existing building(bldg#2) with a 400A underground feeder. An additon is required to the building#2. Due to that total service required is 600A. Can I add a second 200A underground feeder to building#2 while the previous 400A underground feeder is stil there? This is for Ontario Canada. Do not mixup with Rule6-102 whic is applicable for multiple utility services. In my case utility meter is in bldg#1. No more utility meters are required for bldg#2.

Joined: Jun 2006
Posts: 613
M
Member
The answer lies in part with the utility if the second building is metered by them. BC Hydro does not like 2 meters for the same customer space.
If not the Ontario Authority might require demarking the area the other feeder supplies. Nothing worse than cross wiring a place from 2 panels.

Is the addition part of the same occupancy? If so maybe dedicating the new 200 to the addition.

I can't think of a code rule that prevents what you are planning. Certainly the need to disconnect the entire building in a fire might need to be addressed and lableing could be very important IE a sign at each panel stating there is another panel and at the supply end too.

Joined: Jul 2005
Posts: 183
J
Member
if this is a 208 volt feeder you could consider retaining single feeder and stepping up to 600 volt at building 1 and back down to 208 at building 2, which would give you the capacity. But if the feeder is already 600 volts, then I guess its back to second feeder.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,722
Joined: October 2000
Top Posters(30 Days)
BigB 7
triple 3
Popular Topics(Views)
302,738 Are you busy
231,969 Re: Forum
216,687 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5