#199292 - 02/19/11 01:53 PM Transformer wiring  
SJT  Offline
Member
Joined: Jul 2002
Posts: 241
PATCHOGUE, N.Y.
In regard to the NEC, could a 225KVA transformer be used to only feed a 200 amp/208 V 3 phase panel with a main breaker. If such a transformer was to be used, then what size primary protection would be needed? Would I wire it as if it were a 75KVA transformer and rate the primary and secondary accordingly? It's a strange request from a customer. In the future he may run the proper size primary and secondary conductors, to get the max out of the 225 KVA trans.
Thanks - Good Day
SJT


2017 / 2014 NEC & Related Books and Study Guides

#199300 - 02/19/11 05:59 PM Re: Transformer wiring [Re: SJT]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,103
Estero,Fl,usa
The way I understand it you use primary protection that protects the transformer and secondary protection to protect the installed secondary conductors.


Greg Fretwell

#199307 - 02/19/11 11:02 PM Re: Transformer wiring [Re: SJT]  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Need to know how long the Secondary conductors to see if they qualify for the 10' rule mentioned in 240.21(C)(2) or possibly 240.21(C)(3) or 240.21(C)(3). Is it a single voltage secondary qualifying under 240.21(C)(1)? Basically if the xformer is has 225 KVA capacity and you only want to use it at 75KVA there is no problem and the sizing of the primary conductors should be sized to match the secondary load taking in to considration the voltage ratio and maybe an extra 25% would be a good idea to keep the fuses from clearing on start up. There is no need to protect the secondary of the xformer, just the secondary conductors.

Last edited by George Little; 02/19/11 11:04 PM. Reason: Edited for added thought:)

George Little

#199322 - 02/20/11 01:03 PM Re: Transformer wiring [Re: George Little]  
SJT  Offline
Member
Joined: Jul 2002
Posts: 241
PATCHOGUE, N.Y.
Thanks,
I never wired a large transformer to a smaller rating than what it could put out.
Sounds like I'll be OK. I have to check the connection points for the x1, H1, etc. to make sure we use the proper lugs and bolt sizes.


#199667 - 03/04/11 04:20 AM Re: Transformer wiring [Re: SJT]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
On the economics....

A 225 kVA XFMR is huge. Regardless of the true load it will bleed energy to sustain its magnetic circuit.

Correct sizing would mean a XFMR of 75kVA.

So you're bleeding off 225/75 = 3 times as much parasitic losses as would be nominal.

Do run your calculations.

BTW 3 is the lower bound.

Power cost being what it is -- you'd very likely be much better off scrapping/ reselling the gear and downsizing to a new/used transformer.

Talk to Salinger and others in the used electrical equipment market. You'll have your eyes opened.

http://www.salingerelectric.com/



Tesla


Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 15 (0.003s) Memory: 0.7696 MB (Peak: 0.9102 MB) Zlib enabled. Server Time: 2017-08-17 17:25:10 UTC