#198101 01/12/11 08:24 PM
Joined: Aug 2006
Posts: 356
Niko Offline OP
Member
I have a client who has 3 UPS system with a total 10KVA capacity. They currently have a 30Amp feeder with a Subpanel in the communication room.
They have asked me to install a 60Amp feeder for additional UPS units.

here are the question/s that i have.
>I assume i need to have a disconnect within site of the UPS units? Right?
>I will size the feeders to 125%?
>Existing, the UPS feeds the Existing sub panel by a SOO cord, is that O.K.

Thank you for your input


Be kind to your neighbor, he knows where you live

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Niko #198116 01/12/11 11:44 PM
Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
Niko:

Yes to the disconnect.
125% is OK
Possibly OK, but more info is needed. Is the connection from the UPS via a cord cap? Is there frequent 'swapping' of the UPS? IF yes, then the cord could be acceptable.



John
HotLine1 #198117 01/13/11 12:57 AM
Joined: Aug 2006
Posts: 356
Niko Offline OP
Member
There is no frequent swapping of UPS. Currently the UPS is cord & cap connected to the feeder receptacle sized 6AWG then the UPS feeds the subpanel sized 6AWG cord.