Joined: Jul 2004
Posts: 787
L
Member
Is there room to install three 40 A solid link disconnects in the laundry room? Could they all be tied together with a piece of all thread so they all operate together?

LarryC #196976 11/03/10 04:42 PM
Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
"All thread" is not a "listed handle tie" so that would be a no.


Greg Fretwell
Joined: Nov 2002
Posts: 244
W
Member
I wonder if 6 pole pull-outs similar to the the cheapie air conditioner
disconnects are available. If not, it seems it's a ripe time to market something like that.

Joined: Jun 2004
Posts: 1,273
T
Member
Economically, does it make sense to use a mechanically held lighting contactor? The idea being that a simple toggle switch would throw six poles.

I remember 20A and 30A rating contactors by SqD.

Is any NEMA player coming out with a sweet solution for this application?


Tesla
Tesla #196986 11/03/10 09:35 PM
Joined: Nov 2000
Posts: 2,148
R
Member
You can't use contactors as disconnects.


Don(resqcapt19)
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Guess a sub-panel with a 'main' and three branch CBs is a way to go.

The lock-out (if needed by placement) could be installed on the 'main'.
(Two pole like may be used on an oven/range)

Oddly, I only came accross one job with this type unit about 2 years ago, the Ec was debating how to do this when I was there for a rough, and that job is still at a standstill ($$$$) Strange thing was the house has a 150 amp service!



John
Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
I would be interested in the load calc that would allow a 110 a water heater on a 150a service. What kind of range and HVAC equipment do they have?


Greg Fretwell
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Greg:
This is a resi that has an addition, with a service upgrade to 400 amp. The job has been at a standstill for quite some time (1 1/2 to 2 years) due to $$$$. The EC at the time was basically a lost soul with a few items, the WHtr only one of them.



John
Joined: Feb 2002
Posts: 2,233
H
Member
Greg,

I agree that a sub panel by the water heater would be the best option. However what if there is no room? Say the new water heater is in a closet with no room for a sub panel? Then what?

Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
That is the same problem we have with air handlers. The AHJ has to make up his mind, do we waive 110.26 or the "within sight" rule. I guess that is why we make the big bucks wink


Greg Fretwell