2011 code nec #196793 10/27/10 03:37 PM
Joined: Oct 2010
Posts: 2
N
noshorts73 Offline OP
New Member
anyone hear that they are going back to using 75 degree column for ser/seu instead of 60 degree

2017 / 2014 NEC & Related Books and Study Guides
Re: 2011 code nec [Re: noshorts73] #197422 11/27/10 06:59 AM
Joined: Feb 2003
Posts: 939
F
frenchelectrican Offline
Member
Originally Posted by noshorts73
anyone hear that they are going back to using 75 degree column for ser/seu instead of 60 degree


AFAIK not yet until someone do get the 2011 NEC code book with the infomation on SER/SEU cable so hold on until someone will get that infomation and post it for ya.

Merci,
Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Re: 2011 code nec [Re: frenchelectrican] #197425 11/27/10 10:49 AM
Joined: Apr 2002
Posts: 7,235
HotLine1 Offline
Member
From 2011 NEC Article 338.10 (B) 3 & 4:

"(3) Temperature Limitations. Type SE service-entrance
cable used to supply appliances shall not be subject to conductor
temperatures in excess of the temperature specified
for the type of insulation involved.
(4) Installation Methods for Branch Circuits and Feeders.
(a) Interior Installations. In addition to the provisions
of this article, Type SE service-entrance cable used for interior
wiring shall comply with the installation requirements
of Part II of Article 334, excluding 334.80.
Where installed in thermal insulation, the ampacity shall
be in accordance with the 60C (140F) conductor temperature
rating. The maximum conductor temperature rating
shall be permitted to be used for ampacity adjustment and
correction purposes, if the final derated ampacity does not
exceed that for a 60C (140F) rated conductor.
Informational Note No. 1: See 310.15(A)(3) for temperature
limitation of conductors.
Informational Note No. 2: For the installation of main
power feeder conductors in dwelling units refer to
310.15(B)(7).
(b) Exterior Installations. In addition to the provisions
of this article, service-entrance cable used for feeders or
branch circuits, where installed as exterior wiring, shall be
installed in accordance with Part I of Article 225. The cable
shall be supported in accordance with 334.30. Type USE
cable installed as underground feeder and branch circuit
cable shall comply with Part II of Article 340.



John

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 236
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,745 Are you busy
209,659 Re: Forum
197,004 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3