#196500 10/09/10 07:55 AM
Joined: Aug 2010
Posts: 7
M
New Member
Hello!!

Could I use a Tray Cable (TC) certified CSA without the use of a cable tray in an industrial equipment?or I need to use another type of cable?

Thanks!

Joined: Mar 2004
Posts: 947
T
twh Offline
Member
Table 19 shows TC cable as suitable for direct earth burial with protection if it's marked for that use (Table 19, Note 25).

If you run TC cable in a cable tray, you need to get from the tray to the equipment the cable serves. 12-2202(2) covers that by allowing its use in conduit where it isn't in the cable tray.

Other than that, I think you need to use different cable.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 812
Joined: April 2004
Top Posters(30 Days)
Jim M 5
Trumpy 4
Popular Topics(Views)
297,348 Are you busy
228,231 Re: Forum
213,133 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5