#196500 - 10/09/10 06:55 AM Tray Cable  
michelebacocchia  Offline
New Member
Joined: Aug 2010
Posts: 7
Italy
Hello!!

Could I use a Tray Cable (TC) certified CSA without the use of a cable tray in an industrial equipment?or I need to use another type of cable?

Thanks!


Tools for Electricians:

#196507 - 10/09/10 01:55 PM Re: Tray Cable [Re: michelebacocchia]  
twh  Offline
Member
Joined: Mar 2004
Posts: 922
Regina, Sask.
Table 19 shows TC cable as suitable for direct earth burial with protection if it's marked for that use (Table 19, Note 25).

If you run TC cable in a cable tray, you need to get from the tray to the equipment the cable serves. 12-2202(2) covers that by allowing its use in conduit where it isn't in the cable tray.

Other than that, I think you need to use different cable.



Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.009s Queries: 15 (0.002s) Memory: 0.7434 MB (Peak: 0.8597 MB) Zlib enabled. Server Time: 2017-12-18 16:50:32 UTC