ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Changing a Bulb
by gfretwell. 07/14/18 03:12 PM
Tray cable?
by gfretwell. 07/11/18 10:18 PM
Eaton Heavy Duty 30A and 60A Safety Switches
by Admin. 07/11/18 09:49 PM
ORTOVOX Recalls Avalanche Transceivers
by Admin. 07/11/18 09:44 PM
Tingle off the water spigot
by gfretwell. 07/08/18 12:58 PM
New in the Gallery:
Plug terminals
Housebilding DIY wiring
Who's Online Now
1 registered members (electure), 39 guests, and 15 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Generators & Mtrs #196468
10/06/10 03:56 PM
10/06/10 03:56 PM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 842
Michigan
150 KW 480 three phase generator.
Whats largest size mtr. it can start with cross the line starter?
Largest size mtr. with soft start.??
Largest size motor with VFD.
I;m looking for a place I can refer to for this info.
Thanks yoopersup

Work Gear for Electricians and the Trades
Re: Generators & Mtrs [Re: Yoopersup] #196473
10/06/10 06:00 PM
10/06/10 06:00 PM
mxslick  Offline
Member
Joined: Oct 2004
Posts: 803
Atomic City, ID USA
Not enough info provided..the real answer will depend on many variables, such as the motor's design and efficiency, and most importantly what kind of mechanical load the motor is driving.

You will need to look at it on a case-by-case basis to be sure your generator can handle the largest motor load.

And the sequence of load pick-up will make a difference.


Stupid should be painful.
Re: Generators & Mtrs [Re: mxslick] #196474
10/06/10 06:19 PM
10/06/10 06:19 PM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
Normally, the factory would supply those stats.

Is the unit asynchronous, synchronous, or synthetic wave form?

What constitutes an unacceptable voltage sag?

What is the duty rating for the alternator?

What is the duty rating for the motor?

Does it start loaded or unloaded?

What are the specs on the VFD?

These are engineering issues best resolved by the factory.


Tesla
Re: Generators & Mtrs [Re: Tesla] #196476
10/06/10 08:16 PM
10/06/10 08:16 PM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 842
Michigan
Is there a site or Computer program all info can be put in answer come out.
I know Generator suppliers well also supply the info. Just looking for a simple way to actess
same info.

Re: Generators & Mtrs [Re: Yoopersup] #196477
10/06/10 08:36 PM
10/06/10 08:36 PM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 842
Michigan
The formula is: Motor HP x KVA per HP x (1000 / (Volts x 1.73)) = LRA. Example: A 20 HP Code G motor connected to 460 Volts requires what LRA? Refer to Chart A and select 6.29 KVA/HP, from Chart A, for Code G. The formula becomes: 20 x 6.29 x (1000 / (460 x 1.73)) = 125.8 x 1.26 = 158.5 = 159 LRA. The generator must produce 159 Amps at 460 Volts, to safely start this motor. Use formula: 1.73 x Volts x Amps x .8 / 1000 for generator KW size.
Found it! heres part of it harts for mtrs. also on it.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,121 Are you busy
185,579 Re: Forum
174,897 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.027s Queries: 15 (0.005s) Memory: 0.9682 MB (Peak: 1.1087 MB) Zlib enabled. Server Time: 2018-07-19 01:48:53 UTC