Generators & Mtrs #196468 10/06/10 02:56 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
150 KW 480 three phase generator.
Whats largest size mtr. it can start with cross the line starter?
Largest size mtr. with soft start.??
Largest size motor with VFD.
I;m looking for a place I can refer to for this info.
Thanks yoopersup

Work Gear for Electricians and the Trades
Re: Generators & Mtrs [Re: Yoopersup] #196473 10/06/10 05:00 PM
Joined: Oct 2004
Posts: 803
mxslick Offline
Member
Not enough info provided..the real answer will depend on many variables, such as the motor's design and efficiency, and most importantly what kind of mechanical load the motor is driving.

You will need to look at it on a case-by-case basis to be sure your generator can handle the largest motor load.

And the sequence of load pick-up will make a difference.


Stupid should be painful.
Re: Generators & Mtrs [Re: mxslick] #196474 10/06/10 05:19 PM
Joined: Jun 2004
Posts: 1,273
T
Tesla Offline
Member
Normally, the factory would supply those stats.

Is the unit asynchronous, synchronous, or synthetic wave form?

What constitutes an unacceptable voltage sag?

What is the duty rating for the alternator?

What is the duty rating for the motor?

Does it start loaded or unloaded?

What are the specs on the VFD?

These are engineering issues best resolved by the factory.


Tesla
Re: Generators & Mtrs [Re: Tesla] #196476 10/06/10 07:16 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
Is there a site or Computer program all info can be put in answer come out.
I know Generator suppliers well also supply the info. Just looking for a simple way to actess
same info.

Re: Generators & Mtrs [Re: Yoopersup] #196477 10/06/10 07:36 PM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
The formula is: Motor HP x KVA per HP x (1000 / (Volts x 1.73)) = LRA. Example: A 20 HP Code G motor connected to 460 Volts requires what LRA? Refer to Chart A and select 6.29 KVA/HP, from Chart A, for Code G. The formula becomes: 20 x 6.29 x (1000 / (460 x 1.73)) = 125.8 x 1.26 = 158.5 = 159 LRA. The generator must produce 159 Amps at 460 Volts, to safely start this motor. Use formula: 1.73 x Volts x Amps x .8 / 1000 for generator KW size.
Found it! heres part of it harts for mtrs. also on it.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
MCosta 3
Popular Topics(Views)
275,442 Are you busy
209,344 Re: Forum
196,623 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3