Dedicated space #196387 09/29/10 12:13 PM
Joined: Jul 2002
Posts: 241
S
SJT Offline OP
Member
There is a brand new job where there is a 4 foot wide Duct ran above switchgear. The way we are reading 110.26(F)(1)(a)says that no Foreign systems are allowed in the 6 foot space above the equipment. The NEC uses the words "shall be dedicated"to the electrical installation. The question is when you see the words "shall be", that means there is No changing that rule. We are going to tell the Design person of this job that there are No options when it deals with Dedicated space. Comments? Thanks - Good Day

2017 / 2014 NEC & Related Books and Study Guides
Re: Dedicated space [Re: SJT] #196388 09/29/10 01:16 PM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Offline
Member
I don't really see any relief, particularly in new construction. They can pull it away from the wall, out beyond the depth of the switch gear and be compliant.
[Linked Image from gfretwell.com]


Greg Fretwell
Re: Dedicated space [Re: gfretwell] #196390 09/29/10 06:38 PM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
The wording is from the floor to 6 feet above the equipment or up to some type of structural ceiling.

We had a similar situation with tons of foreign piping above the gear in a job in downstate Illinois and they installed a concrete slab below the gear and the piping. The AHJ said that a suspended ceiling or drywall wasn't acceptable, but he would accept something "that you could walk on".

BTW, be glad that you're not in Chicago, where the space isn't just above the equipment, but also above the working space.
smile


Ghost307
Re: Dedicated space [Re: ghost307] #196393 09/29/10 07:19 PM
Joined: Apr 2002
Posts: 7,235
HotLine1 Online Content
Member
Ghost:
Who made that call? The electrical AHJ, or the Building AHJ?



John
Re: Dedicated space [Re: HotLine1] #196395 09/29/10 09:49 PM
Joined: Jul 2002
Posts: 241
S
SJT Offline OP
Member
The Electrical AHJ. The job is a union job. It's a major mistake on the builders part.

Re: Dedicated space [Re: SJT] #196399 09/30/10 09:46 AM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
It's in the actual text of the Chicago Electrical Code.

"Dedicated Electrical Space. The space equal to the width and depth including working space of the equipment and extending from the floor to the structural ceiling shall be dedicated to the electrical installation. No piping, ducts, or equipment foreign to the electrical installation shall be located in this zone."


Ghost307
Re: Dedicated space [Re: ghost307] #196403 09/30/10 02:35 PM
Joined: Apr 2002
Posts: 7,235
HotLine1 Online Content
Member
Thank you gentlemen


John
Re: Dedicated space [Re: HotLine1] #196463 10/06/10 08:37 AM
Joined: Feb 2002
Posts: 2,233
H
harold endean Offline
Member
I have seen a job where the only place to put some piping was directly over the service panel. The only way around it was to install a drip pan to prevent and condensation from dripping on electrical panels.

Re: Dedicated space [Re: harold endean] #196466 10/06/10 01:46 PM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Offline
Member
You had to 90-4 that if it was in the 6 foot dedicated space.
There is no code language to support the variance.


Greg Fretwell
Re: Dedicated space [Re: gfretwell] #196467 10/06/10 02:18 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
A job I did a few years back made me pause to think for a moment ...

How often do we find that plumbing, HVAC, and all manner of building components intrude upon "our" space? Then there is the matter of stuff being stored in the 'working space.'

Yet ... in the same building where they just can't keep stuff out of the electric room .... ever notice how the room for the elevator equipment is kept clear? No HVAC, no file boxes, and even the maintenance guy hasn't set up a desk in there.

I wonder why that is ... could the annual inspection have something to do with it?

Along the same lines ... if the offending pipe is part of the fire sprinklers, NEC is overridden by the sprinkler code. Likewise, there are limits as to how much a plumber can move a drain.

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,612 Are you busy
209,544 Re: Forum
196,901 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3