188
17
I see what you are saying now. Old habits are hard to break. Trying to make it work mu old way which saved time and material (rqual dollars saved). I can still do it my way, add one more 12/2 run and make sure I don't parallel my neutrals.
Here's how you can do it:
Ordinary B/W/G Romex brings power to the first 3-way switch, then B/R/W/G continues to the 4-way(s), B/R/W/G to the last 3-way, then B/W/G to the lights. Between the 3-ways. you use the black and red as your 'travelers.'
I like the idea, but I don't like the rule. This has been my standard for years. However,there are times when I will just drop a switch leg. How is it safer? Appears they are just making it easier for the DIY crowd. We have lost our last ally.
I've noticed a few references to 300.3(B). IMO, 300.3(B) does not apply to non-metallic sheathed cable generally. Read a little further and you will come to 300.3(B)(3) which would allow the conductors of a circuit to be in different non-metallic sheathed cables if 300.20(B) is complied with.
Posts: 9,935 Likes: 34
I may be the only fan but in resi, I would think about running smurf from the kludge ceiling box to the switch locations. That eliminates a bunch of problems.
When I was in business, I would always run my feed to a 3 way/(4W) switch to the first box, then leave the last box to go to the light fixture. This way it was always easier to trace out problems. I never had to drop down lights to see if I had a feed in there. I could check for incoming feed at the switch. So now with the new code, it would not be an issue.
P.S. when the new code goes into effect, do you think the AHJ will look at each box to make sure that there is a neutral in there?
If it is the "violation of the week" they will. That seems to be the way things go. The inspectors I have seen will blitz one particular violation (along with the normal look/see) until all of their installers get into line. It is usually right after a seminar where they all talk about it. I agree it will be something that will add some time to your inspections trying to figure out where are the wires are coming from and going to. In one of those big 4 and 5 gang boxes with multiple circuits feeding it, this might really be a trick. Just because there is a neutral, doesn't mean it is the right neutral.
I use Harold's method for three ways and single pole switches. The main reason I do this is to save a couple of trips up & down a ladder, which is my least favorite tool, and I absolutely hate taking down a light fixture just to troubleshoot connections that could have been avoided by running power to the switch location rather than dropping a switch leg from the fixture box.
As far as neutrals at the switch are concerned, I've seen Howard Homeowner use the equipment ground as a current carrying conductor often enough to think that requiring a neutral at the switch location is a good idea. To the average homeowner, the only difference between a grounded conductor (neutral) and a grounding conductor is the insulation. It'll probably take a few code cycles to work out some of the kinks pointed out by others.
I would say that Code writers are preparing the whole land for Title 24 type energy conservation gadgets which are expected to need a grounded conductor.
Otherwise, the demand seems to be a deliberate attempt at wasting copper, time and other materials.
Tesla
Tesla, I agree with you.
That's been a sore spot with me for years; if you search this site you'll find I had a thread long ago, asking if the NEC had lost focus.
The question is just where 'practical safeguarding' and 'good design' part ways. Make no bones about it; many of the 'safety' arguments are dependent upon design choices. (For example, compare the different US and UK approaches to power in bathrooms).
The NEC plainly states that it is not a design manual, and explains that a 'safe' installation might not be the most efficient design, or have any provisions for future changes.
I don't want to get off on a tangent; if we want to discuss this in more depth, perhaps a new thread is in order.
The real reason behind this rule is so that UL can correct a mistake they made when they permitted electronic switching type device to use the EGC as the grounded conductor. The standard permits up to 0.5mA of current on the grounding conductor. While this is not enough to cause a serious shock, it is enough to feel and the reaction to this low level shock may result in injury. For example you it may cause you to fall off a ladder or something like that. I expect that sometime in the not too distant future the UL standard will be changed to prohibit the use of an EGC as a grounded conductor for these devices.