#195179 07/15/10 02:20 AM
Joined: Dec 2006
Posts: 33
W
wacked Offline OP
Member
I was wondering if anybody knows what is the acceptable ambient air temperature for an electrical room. I did a check on a facility that I am an FSR for (that has more heat producing devices...transformers etc after a new addition) Much to my horror the temperature was 45 degrees celcius. Apparently when the construction for this new addition is totally complete there will be remediation concerning this hot electrical room.
The CEC talks about ventilation, but does anybody have a firm number or know where I can find????

Joined: Jul 2005
Posts: 183
J
Member
that is an interesting problem. Check 6-206 (c) which clearly states 30 degrees. Also 4-004 (8) which calls for conductor derating past 30 degrees. And as you pointed out, 2-318.

Joined: Jun 2006
Posts: 613
M
Member
As Jay states 30 degrees. Hotter, and the equipment must be derated.
Wire is derated per table 5A. 45 C is .85


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 806
Joined: October 2004
Top Posters(30 Days)
timmp 3
Popular Topics(Views)
283,074 Are you busy
216,807 Re: Forum
203,189 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5