How are you interpreting “equipment grounding conductors, where installed,” as stated in 250.122[B] when ungrounded conductors are upsized?
Do you consider this as meaning where an EGC is actually pulled in a raceway, or simply where any EGC is present, whether physically pulled or part of a listed cable assembly, such as SER?

It seems that this could possibly be interpreted either way and might allow using an upsized cable assembly containing an equipment-grounding conductor sized only per Table 250.122, as opposed to a raceway where the conductors are pulled and the EGC sized on the ratio of the circular mil area of the upsized ungrounded conductors.
What is your take on this?

TKX

Horizontal Ad
KJay #194783 06/22/10 12:37 PM
Joined: Jul 2004
Posts: 10,004
Likes: 36
G
Member
In a cable, the EGC size gets bigger in proportion to the other conductors getting bigger so 250.122(B) is satisfied.
I assume that is built into the listing standard for all cables.
In the case of SE cable (TYLZ in the white book) it says

Quote
Based upon tests which have been made involving the maximum heating
that can be produced, an uninsulated conductor employed in a service
cable assembly is considered to have the same current-carrying capacity as
the insulated conductors even though it may be smaller in size.


Greg Fretwell
gfretwell #194784 06/22/10 02:58 PM
Joined: Nov 2007
Posts: 764
K
KJay Offline OP
Member
Thank you Greg. Good find on the SE cable listing.
I had considered that the cables must have had this rule applied already, but now that I have thought this through a bit more, it appears that since Table 250.122 is based on overcurrent, not wire size, it wouldn’t have any relevance when over sizing conductors for things such as voltage drop calcs, being that the actual overcurrent protection would normally be lower than the maximum rating of the conductor.
Unfortunately, sometimes I’m not the sharpest tool in the shed.

KJay #194788 06/22/10 05:12 PM
Joined: Jul 2004
Posts: 10,004
Likes: 36
G
Member
The white book is a great resource if you are curious about the listing on a particular product. Unfortunately it usually ends up making you want to actually see the listing standard and U/L charges big bucks for that.
I suppose that is why they give the White Book away for free. wink


Greg Fretwell

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
pcsailor
pcsailor
Minneapolis, MN, USA
Posts: 21
Joined: September 2019
Top Posters(30 Days)
dsk 1
Popular Topics(Views)
337,502 Are you busy
262,890 Re: Forum
243,177 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5