#194635 06/14/10 03:44 PM
Joined: Jun 2007
Posts: 106
M
Member
Correct me if I am wrong but since NMWU has a 60 degree rating, then #6NMWU is only good for 55Amps unless it is part of a residential service? (T.2 of the OESC) I am guessing that a sub panel to the garage would not fall under this classification therefore limiting my amperage rating to 55amps and not 60?


Never trust an electrician with no eyebrows!!
Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Joined: Jun 2006
Posts: 613
M
Member
I think that as long as the Garage is a residential garage and part of a single residential unit, then 60 amps would apply. A residential Garage is not a continuous load and residential services are non continuous loads.
A duplex with a single joint use garage might not qualify.

Talk to the local authority but I think we would allow the greater ampacity as long as the Volt drop does not get rediculous.

Joined: Mar 2004
Posts: 947
T
twh Offline
Member
Isn't it a 55 amp feeder fused at 60 amps per Table 13? The differences are that if the load in the garage is greater than 55 amps, the wire is too small; and, the location of the panel in the garage isn't restricted like a residential service.

Joined: Oct 2010
Posts: 9
S
New Member
good luck finding a 55 amp breaker

Joined: Jun 2006
Posts: 613
M
Member
Twh
Yes you make the most important point. As long as the calculated load is less than 55 amps then the #6 is good and table 13 would allow a 60 amp breaker.