6/3 NMWU amperage rating? #194635
06/14/10 03:44 PM
06/14/10 03:44 PM
M
mr_electrician  Offline OP
Member
Joined: Jun 2007
Posts: 106
London, Ontario
Correct me if I am wrong but since NMWU has a 60 degree rating, then #6NMWU is only good for 55Amps unless it is part of a residential service? (T.2 of the OESC) I am guessing that a sub panel to the garage would not fall under this classification therefore limiting my amperage rating to 55amps and not 60?


Never trust an electrician with no eyebrows!!
Tools for Electricians:
Re: 6/3 NMWU amperage rating? [Re: mr_electrician] #194641
06/14/10 08:06 PM
06/14/10 08:06 PM
M
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
I think that as long as the Garage is a residential garage and part of a single residential unit, then 60 amps would apply. A residential Garage is not a continuous load and residential services are non continuous loads.
A duplex with a single joint use garage might not qualify.

Talk to the local authority but I think we would allow the greater ampacity as long as the Volt drop does not get rediculous.

Re: 6/3 NMWU amperage rating? [Re: mikesh] #194692
06/16/10 01:33 AM
06/16/10 01:33 AM
T
twh  Offline
Member
Joined: Mar 2004
Posts: 928
Regina, Sask.
Isn't it a 55 amp feeder fused at 60 amps per Table 13? The differences are that if the load in the garage is greater than 55 amps, the wire is too small; and, the location of the panel in the garage isn't restricted like a residential service.

Re: 6/3 NMWU amperage rating? [Re: twh] #197138
11/10/10 10:00 PM
11/10/10 10:00 PM
S
swoop  Offline
New Member
Joined: Oct 2010
Posts: 9
ontario
good luck finding a 55 amp breaker

Re: 6/3 NMWU amperage rating? [Re: swoop] #197160
11/12/10 03:19 PM
11/12/10 03:19 PM
M
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
Twh
Yes you make the most important point. As long as the calculated load is less than 55 amps then the #6 is good and table 13 would allow a 60 amp breaker.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
245,910 Are you busy
182,968 Re: Forum
172,779 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 15 (0.004s) Memory: 0.9674 MB (Peak: 1.1080 MB) Zlib enabled. Server Time: 2018-04-24 18:11:32 UTC