Electricians revenge
0 members (), 205 guests, and 12 robots.
#194010 05/04/10 11:08 PM
twh Offline OP
What type of switch is best for an appliance garage? Is there a limit switch that has a 20 amp rating?
twh #194014 05/05/10 12:07 AM
to switch what twh?
~S~
sparky #194016 05/05/10 01:32 AM
twh Offline OP
To switch the receptacle.
An appliance garage is a box with doors on a kitchen counter where people put things like toasters and food processors. The receptacle has to be off if the door isn't open.
twh #194017 05/05/10 03:22 AM
I would want the limit switch to control a contactor in an application like that. I would be inclined to have a thermal switch in series with it too.
Joe
twh #194018 05/05/10 03:22 AM
why does the receptacles have to be OFF? my first time hearing this.
twh #194019 05/05/10 03:23 AM
F
I think I know what you are refering to this and just a suggest but a door jamb switch may work for your useage but the curpit is the rating of jamb switch IIRC it will be about either 5 or 12 amps depending on what model you get.
Merci,Marc
The OP is in Canada. It is code up here for the receptacle be off if the door is shut.
Square D has a class 9006 L100/300 series rated for 20 amp continuous (page 21-34, digest 175) but you are going to pay for it. Other manufacturers have similar but I don't have current catalogues. As far as size goes I would go for the small switch (less damage to the cabinet over time) to a relay, it may be about similar in bulk. I am glad we don't have that requirement.
I'm going to move this to the Canadian Code Section.....may get the appropriate responses there.
twh Offline OP
I thought it was a normal thing for residential work, but the wholesalers haven't heard of such a thing, and I have to do two. At the first I used a limit switch and a 20 amp relay, because the wholesalers told me a 20 amp limit switch isn't available. Now I know better and I think the switch alone is a better option.
Thanks sabrown.