Would anyone know how to size the resistors on a Wye start/delta run closed transition starter? Say for a 50 Hp 230V motor?

Horizontal Ad
Joined: Oct 2000
Posts: 2,724
Likes: 1
Broom Pusher and
Member
I believe the Resistors would be sized ("size" = Resistance value - in Ohms), so as to allow the same level of Current that the "Wye" configuration does.

Example:
Motor's FLA = 130 Amps
Starting (Wye Connection) Ampere = +/- 75 Amps
Resistors are sized to allow +/- 75 Amps at rated Voltage.

I am not 100% sure on this, so let me find some references, then reply back.

Scott


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Joined: Dec 2003
Posts: 36
D
Member
That makes sense to me. The smaller you make them the closer to normal current you have. The next question is Watt ratings. The resistors are only in the circuit for a split second in the transition between wye and delta so would you need full power ratings(Peak I^2 R) on them?


Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Top Posters(30 Days)
dsk 1
Popular Topics(Views)
555,618 Are you busy
430,359 Re: Forum
399,814 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5