#193710 04/14/10 11:56 PM
Joined: Jul 2002
Posts: 241
S
SJT Offline OP
Member
The Space located 6'above Panels, Services, Motor Control centers, and Distribution Equipment and as wide as the Equipment is solely for the Electrician, right? No piping or other ducts etc. are allowed in this space. Does the 6'rule (110.26) also apply to disconnects, or are they exempt from the rule? Thanks

Horizontal Ad
Joined: Mar 2005
Posts: 399
A
Member
It depends. Check 110.26 (E)


Alan--
If it was easy, anyone could do it.
Joined: Jul 2004
Posts: 10,024
Likes: 37
G
Member
You also have the issue of dedicated electrical space above the 6'6 working space.

Quote
(1) Indoor. Indoor installations shall comply with 110.26(F)(1)(a) through (F)(1)(d).
(a) Dedicated Electrical Space. The space equal to the width and depth of the equipment and extending from the floor to a height of 1.8 m (6 ft) above the equipment or to the structural ceiling, whichever is lower, shall be dedicated to the electrical installation. No piping, ducts, leak protection apparatus, or other equipment foreign to the electrical installation shall be located in this zone.
Exception: Suspended ceilings with removable panels shall be permitted within the 1.8-m (6-ft) zone.
(b) Foreign Systems. The area above the dedicated space required by 110.26(F)(1)(a) shall be permitted to contain foreign systems, provided protection is installed to avoid damage to the electrical equipment from condensation, leaks, or breaks in such foreign systems.
(c) Sprinkler Protection. Sprinkler protection shall be permitted for the dedicated space where the piping complies with this section.
(d) Suspended Ceilings. A dropped, suspended, or similar ceiling that does not add strength to the building structure shall not be considered a structural ceiling.


Greg Fretwell
Joined: Mar 2005
Posts: 399
A
Member
110.26(E) applies ONLY to service equipment, switchboards, panelboards, or motor control centers.
Does the disconnect function as one of those items ?
Yes or no, determines if the rule applies, i.e. it depends.


Alan--
If it was easy, anyone could do it.
Joined: Jul 2004
Posts: 10,024
Likes: 37
G
Member
That is always the question. When do you apply "working space" to disconnects? and the answer seems to be which disconnect and what AHJ are you talking to.


Greg Fretwell
Joined: Jul 2002
Posts: 241
S
SJT Offline OP
Member
It can get crowded out there in a Mechanical room, between the plumbers pipes, HVAC guys, and technicians. It's good those clearance rules out there. It's almost like picturing an invisible 3D frame over your Equipment and claiming that territory.

Joined: Mar 2003
Posts: 849
Y
Member
I'd say fuseable disconnects & controllers come into that because you can change the fuses while engerized.

Horizontal Ad
Joined: Feb 2002
Posts: 2,233
H
Member
I always though that an HVAC disconnect(disco) would need work space clearances (WSC) because they have to be serviced. Now the Dep. of Community Affairs tell me that the HVAC disco does not need WSC because it is not "serviceable equipment". I said, OK maybe that would be so if there are no fuses, but I believe if there are fuses, you need WSC. That would be the way I call it if I see it.

Joined: Jul 2004
Posts: 10,024
Likes: 37
G
Member
The way it has been explained to me is that a HVAC service tech might need to test the voltage on the line side of the disconnect. I could make that argument for every switch in the house.

Most fused disconnects (all?) have the fuse on the load side of the disconnect so nobody should need to handle an energized fuse.


Greg Fretwell
Joined: Mar 2003
Posts: 849
Y
Member
If you read 110.26 (a) Fused disconnects & Controllers (changing heaters ect )come under it. If you read in the handbook (I know its not the code) explaination it covers thoses items.
just my call.

Last edited by Yoopersup; 04/26/10 09:08 PM.
Page 1 of 2 1 2

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Top Posters(30 Days)
Trumpy 5
davey 1
Popular Topics(Views)
550,222 Are you busy
424,859 Re: Forum
396,174 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5