Common neutral question #193642 04/12/10 08:02 AM
Joined: Oct 2002
Posts: 830
S
sparkync Offline OP
Member
I have a piece of commercial kitchen equipment that requires 2 120 volt circuits. Each pulls 1750 watts. Is there anything wrong with pulling 12/3 mc cable with a common neutral to this equipment, provided I put a double pole breaker on the circuit? Thanks...

Work Gear for Electricians and the Trades
Re: Common neutral question [Re: sparkync] #193645 04/12/10 09:07 AM
Joined: Feb 2008
Posts: 165
R
Rewire Offline
Member
How is the connection made to the equipment?Unless the manufacturer says don't I see no NEC issue with the what you want to do.

Re: Common neutral question [Re: Rewire] #193648 04/12/10 10:35 AM
Joined: Oct 2002
Posts: 830
S
sparkync Offline OP
Member
The equipment plugs directly into a regular 120 volt outlet. They will both probably be used at the same time.
Thanks..

Re: Common neutral question [Re: sparkync] #193650 04/12/10 10:51 AM
Joined: Oct 2006
Posts: 745
E
EV607797 Offline
Member
I see no problem at all. Even if only one of the items is used, the neutral will carry 100% of the load. If both are used, then the current will be equally divided among the hot legs with the neutral carrying any imbalance.


---Ed---

"But the guy at Home Depot said it would work."
Re: Common neutral question [Re: EV607797] #193709 04/14/10 10:23 PM
Joined: Jul 2002
Posts: 241
S
SJT Offline
Member
I am not a big fan of common neutrals. If one circuit is overloaded for whatever reason, it also takes out the other circuit, being it's on a 2 pole breaker. I would stay with a neutral for each circuit, especially kitchen equipment.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
pcsailor
pcsailor
Minneapolis, MN, USA
Posts: 21
Joined: September 2019
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,704 Are you busy
209,627 Re: Forum
196,966 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3