ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
250.104
by gfretwell. 02/16/19 01:08 PM
PurpleAir Recalls Power Supply Units
by Admin. 02/14/19 08:43 PM
Utility Company Programs
by katty81. 02/14/19 11:11 AM
AFDD's coming to the UK
by Trumpy. 02/14/19 12:29 AM
Delta Electronics Recalls Solar Inverters
by electech. 02/13/19 10:26 AM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 5 guests, and 13 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Common neutral question #193642
04/12/10 08:02 AM
04/12/10 08:02 AM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
I have a piece of commercial kitchen equipment that requires 2 120 volt circuits. Each pulls 1750 watts. Is there anything wrong with pulling 12/3 mc cable with a common neutral to this equipment, provided I put a double pole breaker on the circuit? Thanks...

Work Gear for Electricians and the Trades
Re: Common neutral question [Re: sparkync] #193645
04/12/10 09:07 AM
04/12/10 09:07 AM
R
Rewire  Offline
Member
Joined: Feb 2008
Posts: 165
Missouri
How is the connection made to the equipment?Unless the manufacturer says don't I see no NEC issue with the what you want to do.

Re: Common neutral question [Re: Rewire] #193648
04/12/10 10:35 AM
04/12/10 10:35 AM
S
sparkync  Offline OP
Member
Joined: Oct 2002
Posts: 830
NC
The equipment plugs directly into a regular 120 volt outlet. They will both probably be used at the same time.
Thanks..

Re: Common neutral question [Re: sparkync] #193650
04/12/10 10:51 AM
04/12/10 10:51 AM
E
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
I see no problem at all. Even if only one of the items is used, the neutral will carry 100% of the load. If both are used, then the current will be equally divided among the hot legs with the neutral carrying any imbalance.


---Ed---

"But the guy at Home Depot said it would work."
Re: Common neutral question [Re: EV607797] #193709
04/14/10 10:23 PM
04/14/10 10:23 PM
S
SJT  Offline
Member
Joined: Jul 2002
Posts: 241
PATCHOGUE, N.Y.
I am not a big fan of common neutrals. If one circuit is overloaded for whatever reason, it also takes out the other circuit, being it's on a 2 pole breaker. I would stay with a neutral for each circuit, especially kitchen equipment.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
andey 3
Popular Topics(Views)
253,228 Are you busy
189,876 Re: Forum
179,581 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 15 (0.005s) Memory: 0.9674 MB (Peak: 1.1070 MB) Zlib enabled. Server Time: 2019-02-18 08:16:03 UTC