changeing colors blk,red,wht. to Blk ,Green, White #192828 03/05/10 10:40 AM
Joined: Mar 2003
Posts: 849
Y
Yoopersup Offline OP
Member
Interesting situation! Partial remodel of Existing kitchen area. Electrical only. Several Ungrounded outlets on 3 wire ungrounded #12 . New #12 circuits from Panel to ist outlets easy to get without tearing walls apart. Rest are big deal!! One wall can get new outlet boxes & romex in OK.
Other wall 2 older ungrounded outlets with 3 wire Blk,Red , Wht. Can you Change Red to Ground(Strip or tape green) tie into existing box with new romex feed thoses two. Just looking for opinions?
Yoopers

2017 / 2014 NEC & Related Books and Study Guides
Re: changeing colors blk,red,wht. to Blk ,Green, White [Re: Yoopersup] #192830 03/05/10 02:16 PM
Joined: Mar 2005
Posts: 399
A
Alan Nadon Offline
Member
You might get away with it , but it does violate 310.12 reference to 250.119 NEC 2008.


Alan--
If it was easy, anyone could do it.
Re: changeing colors blk,red,wht. to Blk ,Green, White [Re: Alan Nadon] #192834 03/05/10 03:11 PM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Online Content
Member
I agree it is a technical violation but if you stripped the red wire as far back as you can see it maybe with a green wrap of tape to avoid any possible confusion, I think the safety aspect of grounded outlets outweighs the violation.


Greg Fretwell
Re: changeing colors blk,red,wht. to Blk ,Green, White [Re: gfretwell] #192842 03/05/10 10:39 PM
Joined: Nov 2007
Posts: 763
K
KJay Offline
Member
If it a non industrial installation, I'm not sure how you could insure that only qualified individuals will service this installation, but maybe you could talk to your AHJ and see if he'll agree to let you use one of the methods for identifying the grounding conductor in multiconductor cables listed in 250.119[B].
These basically mimic what was just outlined in the post above anyway, that is, either stripping the exposed conductor bare, taping it green or coloring the exposed insulation green at every point where the wire is accssible.



Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 69
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,614 Are you busy
209,547 Re: Forum
196,903 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3