Can a ambiance low voltage 300 watt transformer for under cabinet lighting be mounted in a attic.

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Nov 2007
Posts: 764
K
Member
My best guess would be probably not, since a lot of small transformers seem to have warnings about installing them in areas like that.

The only mention about Ambiance transformers in high ambient temps I can find on the Seagull website is in regard to their 24-volt dual output model 9465-12 transformer, which the specs say... "24v 1000w model has a high ambient rating for use in areas up to 55*C (132*F)".
The thing is though, that even around here, in the summer months an attic can easily get well over 132*F, so that could lead to issues.
I would maybe shoot an email to Seagull and see what they have to say.

BTW, check out the price on that 9465-12 transformer... MSRP: $585.75 shocked

Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Beside the mfg instructions, and opinion, I would suggest an inquiry to the local AHJ, as he is the persom that may or may not accept the install. Knowing the ambient temp in your area, and any relevant chatacteristice of the attic you plan the install in will help (attic ventilation, soffit vents, etc)


John
Joined: Feb 2008
Posts: 165
R
Member
Is the transformer listed for the location? The first thing that comes to mind is ambient temperatures in the attic being greater than the listing of the transformer.

Joined: Feb 2006
Posts: 78
L
Member
At the time I posted this I hadn't purchased the transformer and was looking for input, I know have the transformer and it does state not to exceed 120 degrees so I mounted it in a walk in pantry closet. Thanks for the input.