ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Calling all Non-US members!! (Non-US only)
by Bill Addiss. 08/13/18 05:52 PM
Upgrade the old panel
by gfretwell. 08/13/18 12:20 AM
depth of duckbank
by ghost307. 08/12/18 09:26 PM
Section 179 vehicle purchases
by BigB. 08/05/18 01:06 PM
Don't you buy this stuff
by BigB. 08/05/18 01:00 PM
New in the Gallery:
Plug terminals
Housebilding DIY wiring
Who's Online Now
0 registered members (), 9 guests, and 24 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
choosing terminal lugs #191253
12/23/09 02:34 AM
12/23/09 02:34 AM
H
HongYen  Offline OP
New Member
Joined: Dec 2009
Posts: 1
china
Hi everyone,

I'm trying to choose a suitable terminal lug for my application.

To conduct 550A rms in a 1.06mm diameter wire, it was calculated to require 50mm^2 of wire.

However, when i went to find terminal lugs, AWG 1/0 lugs can only take about 200A.

550A rms is not a continuous working current, but will be reached as certain operation points.

How should i choose terminal lugs for 550A rms please?

Any comments/suggestions appreciated.

Regards,
mactech001

Tools for Electricians:
Re: choosing terminal lugs [Re: HongYen] #191266
12/23/09 01:13 PM
12/23/09 01:13 PM
S
sabrown  Offline
Member
Joined: Dec 2002
Posts: 302
Ogden, Utah, USA
My answer is based on several assumptions and the National Electrical Code.

Seems to me that you need to go back and check your calculations or I am misunderstanding what you are asking. Without doing calculations on the wire, but looking up 550 amps on the tables, it would require a 1250 kcmil (32.74 mm dia, 633 mm^2) conductor.

A 1.06 mm dia wire is 18 AWG and rated for 14 amps at 90 degrees C, while a 50 mm^2 are cable would be closest to a #1/0 AWG and rated for 150 amps at 75 degrees C.

So are we dealing with a Motor or someother device with an in rush current of 550 amps? It makes a huge difference.

Is this is for a product that is going into production, or a one time sizing? If production you need to talk to someone above you for direction, you may end up with something that is non-listable, but may be a hazard o life and property.

I am making the assumption that you are a young (in the feild, not neccesarily age or time engineering in other areas of the feild) engineer (based on your use of the term RMS), not just someone unconnected with the electrical field. If you are a young engineer, please find a good old salt of the earth licensed electrician (or an electrical engineer in the feild) to work with to help you with all the things they don't teach us in school in this area of the electrical field. Specific education in this area is needed and it helps alot to get out there and get your hands dirty. Also, if you are an engineer stick around and learn. If you are not, you are way in over your head.

I sure hope that the little catch phrases translate well, just seeing that you are from China.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
248,578 Are you busy
186,311 Re: Forum
175,771 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 15 (0.004s) Memory: 0.9435 MB (Peak: 1.0586 MB) Zlib enabled. Server Time: 2018-08-17 18:46:38 UTC