ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Advertisement:-Left
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 412 guests, and 15 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Aug 2006
Posts: 356
Niko Offline OP
Member
I was having a discussion with one of the inspectors on the size of a Neutral for a 200Amp service. My comments was that a 200Amp single phase 3 wire service only needs a minimum of (2) 2/0 for the ungrounded and one #4 for the grounded conductor. But the inspector argued that all three conductors have to be 2/0.
we agreed that the grounded conductor of a multiwire branch circuit will carry the unbalanced load only but he would not agree that a residential service is basically a multiwire system and the grounded conductor will carry the unbalanced load only. In a 200A service the maximum current that the grounded conductor will ever see is 100Amps.

Am I missing anyhting?


Be kind to your neighbor, he knows where you live

Horizontal Ad
Joined: Jul 2004
Posts: 10,020
Likes: 37
G
Member
In a practical sense the greatest amount of neutral current might be 100a but the theoretical max is 200a.
You get your guidance from 250.24(C)(1)

Quote
(1) Routing and Sizing. This conductor shall be routed with the phase conductors and shall not be smaller than the required grounding electrode conductor specified in Table 250.66 but shall not be required to be larger than the largest ungrounded service-entrance phase conductor. In addition, for service-entrance phase conductors larger than 1100 kcmil copper or 1750 kcmil aluminum, the grounded conductor shall not be smaller than 121/2 percent of the area of the largest service-entrance phase conductor. The grounded conductor of a 3-phase, 3-wire delta service shall have an ampacity not less than that of the ungrounded conductors.


Plus the 220.61 calculations


Greg Fretwell
Joined: Aug 2006
Posts: 356
Niko Offline OP
Member
Greg,
how can it be 200Amps in theory for a single phase 120V-240V system?

Thanks.



Be kind to your neighbor, he knows where you live

Joined: Aug 2002
Posts: 402
J
Member
A 200 amp service can supply 200 amp from each hot. That means that if one hot is 0 amps then the neutral could be 200 amps from the other hot.

Joined: Jan 2005
Posts: 5,476
Likes: 3
Cat Servant
Member
I think you confused 'grounded' with 'grounding' conductor.

While there are circumstances were we can reduce the size of the neutral, a service isn't usually one of them. You would have to be able to show that the bulk of the load was from 240v circuits, and size the neutral to serve ALL of the 120v. loads.

Joined: Sep 2004
Posts: 68
H
Member
Niko,
I believe that you are correct. If one does a load calculation for a typical residential service, even for a large house, the maximum 120-volt loads are very likely well below 100 amps. Then if you assume that all those loads are on one phase, which would never happen, a #4 copper would certainly be plenty large.

However, when one tries to do something that is out of the ordinary or unusual the typical reaction from other tradesmen or inspectors is at least surprise or disbelief. I do agree with you that the neutral can be sized to the maximum unbalanced load if it meets the other requirement for minmum size of ground.

Be prepared to show your service calculation if you want to win that arguement with an inspector. A more common size for a neutral in a residence is two sizes smaller than the phase conductors. This provides plenty of capacity for future circuits and avoids wasting your time arguing. I suppose the bottom line is the value of your time to do the load calculation and discuss this with an inspector versus the amount you save in wire costs. If the cable length is significant, then it might be worth your while to have the discussion in advance with the inspector. Good luck.

Joined: Jul 2004
Posts: 10,020
Likes: 37
G
Member
I thought about this a little last night and worst case would be if an installer was thinking about heat in AFCI breakers and he got creative in his shiny new (2008 compliant) 60 slot panel.
So he wouldn't put two next to each other, skipping every other space. I would hope someone would catch that but who knows?
If you did want to follow that strategy, checkerboard them. The ones on the odd side, one space off of the ones on the even side. That would give you plenty of breathing room and still balance the load.

BTW I couldn't get NFPA to admit there was a heat problem with a panel full of AFCIs so that may not even be an issue. I guess they never saw a panel in an un-air conditioned garage


Greg Fretwell
Horizontal Ad
Joined: Aug 2006
Posts: 356
Niko Offline OP
Member
I am not trying to save or argue with anyone. My point is that in a residential setting 200Amp main panel the Neutral can be down sized #4 minimum to handle the 100Amps.

Well having said that, I guess it is possible in a 40 space panel if every other breaker has 10Amps of load then the Neutral will see 200Amps.


Be kind to your neighbor, he knows where you live

Joined: Jul 2007
Posts: 1,337
S
Member
A neutral can be smaller per code and if the AHJ is Kosher with it. I always size my grounded conductor the same size as my grounded conductor. Saves times and doesn't impede future needs.

In theory, 200 amps can be impressed on the neutral providing all the electrical draw is on one leg and nothing is drawing on the other.


"Live Awesome!" - Kevin Carosa

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 