ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 175 guests, and 7 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#190353 11/12/09 05:16 PM
Joined: Mar 2005
Posts: 240
Member
I have a 400Amp service with 2 200Amp disconects. Can I put doouble barel lugs on 1 disconect to feed 1 200Amp panel and feed 100Amp back fed breaker.
Thanks H2O

Work Gear for Electricians and the Trades

Workgear for Electricians

Joined: Jan 2004
Posts: 1,507
G
Member
My answer would be yes assuming your load is appropriate. Assuming also you are not overloading the 200a. overcurrent device and the 100a breaker is secured in the panel by a Listed clip.


George Little
Joined: Jan 2005
Posts: 5,485
Likes: 5
Cat Servant
Member
The only joker in the deck is that the wire to the 100 amp panel should be sized for 200 amps, unless you can apply tap rules to your circumstance. Otherwise, there might be a problem fitting the wire into the breaker.

Joined: Jan 2004
Posts: 1,507
G
Member
Reno- If I'm reading his post correctly, this would be a tap to a 200a Service switch. Since he is on the load side of fusing, we are talking feeder. In his case there are no actual feeder conductor, only double barrel lugs. This happens sometimes. Since he is terminating in a 100a overcurrent device he could use 100a. wire. The code reference could be 240.21(B)(1). There is no way he could overload the 100a. conductors since there protected due to the tap limitation mentioned above.

Last edited by George Little; 11/12/09 08:17 PM. Reason: Big fingers

George Little
Joined: Mar 2005
Posts: 240
Member
thanks guys.
H2o

Joined: Jul 2004
Posts: 10,053
Likes: 40
G
Member
I think Reno may be referring to the raceway requirements and 25' length restrictions for taps. The ampacity part is OK if this is a legal tap.


Greg Fretwell
Joined: Jan 2005
Posts: 5,485
Likes: 5
Cat Servant
Member
Thank you, Greg.

Work Gear for Electricians and the Trades

Workgear for Electricians


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5