Posted By: watersparkfalls 200amp disconect - 11/12/09 09:16 PM
I have a 400Amp service with 2 200Amp disconects. Can I put doouble barel lugs on 1 disconect to feed 1 200Amp panel and feed 100Amp back fed breaker.
Thanks H2O
Posted By: George Little Re: 200amp disconect - 11/12/09 09:47 PM
My answer would be yes assuming your load is appropriate. Assuming also you are not overloading the 200a. overcurrent device and the 100a breaker is secured in the panel by a Listed clip.
Posted By: renosteinke Re: 200amp disconect - 11/12/09 11:12 PM
The only joker in the deck is that the wire to the 100 amp panel should be sized for 200 amps, unless you can apply tap rules to your circumstance. Otherwise, there might be a problem fitting the wire into the breaker.
Posted By: George Little Re: 200amp disconect - 11/13/09 12:16 AM
Reno- If I'm reading his post correctly, this would be a tap to a 200a Service switch. Since he is on the load side of fusing, we are talking feeder. In his case there are no actual feeder conductor, only double barrel lugs. This happens sometimes. Since he is terminating in a 100a overcurrent device he could use 100a. wire. The code reference could be 240.21(B)(1). There is no way he could overload the 100a. conductors since there protected due to the tap limitation mentioned above.
Posted By: watersparkfalls Re: 200amp disconect - 11/13/09 07:12 AM
thanks guys.
H2o
Posted By: gfretwell Re: 200amp disconect - 11/13/09 07:38 AM
I think Reno may be referring to the raceway requirements and 25' length restrictions for taps. The ampacity part is OK if this is a legal tap.
Posted By: renosteinke Re: 200amp disconect - 11/13/09 04:14 PM
Thank you, Greg.