Range cord vs circuit #190138 11/07/09 01:14 PM
Joined: Mar 2005
Posts: 236
watersparkfalls Offline OP
Member
I have an island(slab)with a range in it, I will need to pull thwn through my raceway to feed it, the manufactures specs say it has a maximum amperage of 27.6 amps and requires a 40 amp cord for connection. Can I feed a 40 amp plug with only 30 amps? Seems as an apprentice, my old company got gigged for this exact same thing. What say you?
Thanks,
H20

2017 / 2014 NEC & Related Books and Study Guides
Re: Range cord vs circuit [Re: watersparkfalls] #190143 11/07/09 03:18 PM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Online Content
Member
230.23

Quote
(B) 30-Ampere Branch Circuits. A 30-ampere branch circuit shall be permitted to supply fixed lighting units with heavy-duty lampholders in other than a dwelling unit(s) or utilization equipment in any occupancy. A rating of any one cord-and-plug-connected utilization equipment shall not exceed 80 percent of the branch-circuit ampere rating.


Greg Fretwell
Re: Range cord vs circuit [Re: gfretwell] #190147 11/07/09 04:56 PM
Joined: Nov 2007
Posts: 763
K
KJay Offline
Member
What I have noticed, over the last several years anyway, is how difficult it is sometimes to decipher range manufactures listed installation instructions and electrical requirements.
Often they list a minimum circuit ampacity as well as a minimum conductor size that doesn’t seem to correspond directly to the nameplate rating of the appliance.

I can remember a couple of years ago with one dual-fuel range, the installation instructions said to install a 30A 4-wire receptacle in the location specified on the template, but when I read the actual electrical requirements in the instructions, they stated to use a #8 minimum conductor size for the branch circuit.

Because of this, I always try and get copies of the manufactures installation instructions whenever I get the appliance schedule for a job.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,730 Are you busy
209,645 Re: Forum
196,989 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3