ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
334.80 and fire caulk
by gfretwell. 06/21/18 11:35 AM
Calling all Non-US members!! (Non-US only)
by HotLine1. 06/13/18 01:50 PM
GE Lighting Recalls LED Tube Lamps
by Admin. 06/12/18 09:32 PM
Ketra Recalls Recessed Downlights
by Admin. 06/12/18 09:17 PM
diazed fuses
by Texas_Ranger. 06/11/18 07:31 AM
New in the Gallery:
Plug terminals
Housebilding DIY wiring
Who's Online Now
0 registered members (), 45 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Dimmer Blown Out #189545
10/16/09 08:25 AM
10/16/09 08:25 AM
S
shortcircuit  Offline OP
Member
Joined: Jun 2004
Posts: 608
massachusetts
I use Lutron AY600 and AY1000 watt dimmers alot in residential work. The problem I'm having with some of the jobs is the dimmers are blowing out when the incandecent lamps blow out.

I have had dimmer failure with a simple 60 watt candle bulb in a dining room light, a 75 watt par30 in a recessed light and with a 100 watt bi-pin halogen bulb.

Can anyone recomend a dimmer that can better withstand light bulb blow outs?

Thanks,

shortcircuit

Work Gear for Electricians and the Trades
Re: Dimmer Blown Out [Re: shortcircuit] #189549
10/16/09 12:57 PM
10/16/09 12:57 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,228
Estero,Fl,usa
A lot of the lamp failures I see involve a bolted fault between the stanchions that hold up the filaments. Next time you have one of these carefully break the envelope of the bulb and I bet you will see them welded together.
I don't know what this fault current is but it often trips the breaker.

The fix is probably better lamps but I am not sure where they would come from. Everyone is building to a price point these days, not a performance standard.

An alternative fix might be some kind of supplemental over current protection but if it takes a service call to replace the fuse, you didn't really save much.


Greg Fretwell
Re: Dimmer Blown Out [Re: shortcircuit] #189552
10/16/09 03:05 PM
10/16/09 03:05 PM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,236
SI,New Zealand
short-circuit,
Are these bulbs used in an inverted position (upside-down) by any chance?
I read somewhere some time back that that sort of thing is to be avoided,as it is easier for the broken portion of the filament to bridge the filament stanchions.

As Greg mentioned, there isn't really an easy fix as long as you want to go fusing your switch wires (feeding the lamp circuits.

The only other thing I could suggest is (not sure if they exist in the US) rough service lamps, where the filament has more filament supports than a standard bulb.

Re: Dimmer Blown Out [Re: Trumpy] #189554
10/16/09 03:34 PM
10/16/09 03:34 PM
G
geoff in UK  Offline
Member
Joined: Dec 2002
Posts: 189
UK
I've observed that some good quality bulbs have an internal fuse in the base, which I think can save a lot of problems. I've also seen cheap bulbs fail explosively, showering broken glass and taking out the circuit breaker.

Re: Dimmer Blown Out [Re: geoff in UK] #189556
10/16/09 05:40 PM
10/16/09 05:40 PM
S
shortcircuit  Offline OP
Member
Joined: Jun 2004
Posts: 608
massachusetts
Thanks for the replies guys. I spent hours today reading and researhing this because I have an unhappy customer who doesn't want to pay for the new dimmer or bulbs that have failed on a job with very low use on the installation, maybe 8hrs use.

Trumpy...I used a 1000watt Lutron dimmer on 3 outside bullet style double flood lights with G8 base 120volt 100watt halogen capsule bi-pin style bulbs.

I found some light bulb info in another thread here on this site...

http://members.misty.com/don/bulb1.html#wbs

I also called Philips technical assistance who said the bulb failure would never cause a dimmer to blow out. They said it must have been a power surge/spike or some problem with the dimmer.

I called Lutron technical assistance who said that it is possible that bulb failure in some instances can blow the dimmer.

Both companies offered replacements and Philips said to send the failed bulbs in so they could have a look.

Greg...I have 3 failed bulbs from the job and 1 bulb has evidence of a violent condition when it failed. There are burn marks on the glass inside the bulb and the filament supports have broken apart completely.

I suspect this failed bulb caused the dimmer failure.

shortcircuit




Re: Dimmer Blown Out [Re: shortcircuit] #189612
10/19/09 08:03 PM
10/19/09 08:03 PM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
Someone needs to put a scope on that dimmer.

I suspect that astounding peak transitory voltages are stacking up. It's the dimmer that's causing the spiking.



Tesla
Re: Dimmer Blown Out [Re: Tesla] #189621
10/20/09 12:24 AM
10/20/09 12:24 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,228
Estero,Fl,usa
If those filament supports short it is a bolted fault until something gives and that will usually be the dimmer.
If the breaker trips the dimmer will probably be shorted "on" or the triac could just blow open before the breaker trips.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,236
Joined: July 2002
Show All Member Profiles 
Top Posters(30 Days)
twh 5
Admin 2
Popular Topics(Views)
247,671 Are you busy
184,991 Re: Forum
174,296 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.046s Queries: 15 (0.009s) Memory: 0.9869 MB (Peak: 1.1436 MB) Zlib enabled. Server Time: 2018-06-23 04:32:18 UTC