ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 235 guests, and 27 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
Joined: Mar 2004
Posts: 251
W
Member
As long as every part in the control ckt is rated for what ever voltage ( and current) that is present, its code. It makes no difference as to phase to phase or phase to ground, everything must be rated for the highest voltage found in the ckt. Over current protection must be in place where required. I agree with most that low voltage (24v or 120v) control is much preferred. Robert

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Mar 2008
Posts: 27
G
Member
The mine and mill that I work in were built in the early 1960's. All of the original controls are 480vac delta. Quite alot of them don't have and EGC either, mostly solid wire. Hard part is explaining how the voltage is present on hot and reutrn side of the cicuit with the switch open.

MSHA has it's own set of rules when it comes to electricty, otherwise how could you drag a 200 foot long cable behind a machine running on 480vac? And allow the operator to move it into and out of hangers when it's energized?


Sometimes not getting what you want can be an incredible stroke of luck.
Joined: Mar 2008
Posts: 27
G
Member
PS MSHA electrical is 30 CFR Part 57 Subpart K and 30 CR Part 18


Sometimes not getting what you want can be an incredible stroke of luck.
Joined: Jul 2007
Posts: 1,335
S
Member
Originally Posted by gpsparky
Hard part is explaining how the voltage is present on hot and reutrn side of the cicuit with the switch open.

You are measuring the line voltage between two legs minus the voltage drop from the load that the push button controls, likly a coil.

Look at it as a series circuit. The open contact and presume (never assume) for this dissussion is a very resistive load. It will be in series with the coil. Although the coil resistance is high, it will be much lower then the open contact. In a series circuit, the voltage of the circuit will be the sum of voltage of each load within the circuit. In addition the voltage at each load will be inversly propotional to the resistance of each load. The higher the resistance is of a load, the lower the voltage for the load will be.

If we assign a resistance value to each load, R1 being 10 Gig-ohms (open contact) and R2 was 50,000 ohms (coil), the resistance of R2 makes up only .0000005% of the total resistance of the circuit so the voltage will be 99.9999995% of the total voltage. Being that the line voltage is so high the voltage drop is less across R2. Although it appears that the voltage is the same, when the contact is open, you are actually measuring is the line voltage minus the voltage drop.

A digital voltmeter will likely pick up the voltage but not a analog meter due to its high resistance.


"Live Awesome!" - Kevin Carosa
Joined: Mar 2008
Posts: 27
G
Member
No, actually its because L1 is phase one of the delta and L2 is phase two of the gelta and either one to ground will give you voltage less than 480 if the switch is open


Sometimes not getting what you want can be an incredible stroke of luck.
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
How is this delta grounded. That will be the deciding factor.



Greg Fretwell
Joined: Mar 2008
Posts: 27
G
Member
Delta ground is derived from the primary side of the xfmr at each substation in the plant. I know how it works and my boss found out the hard way when he got zapped by the L2 on a control circuit.

Actually a funny story, him and two other guys were troubleshooting a starter, one had a the L2 in his hand (?), leaned on another guy and then he leaned on the foreman who was in contact with the side of the box. Don't know how they did it, but needless to say they all got a buzz.


Sometimes not getting what you want can be an incredible stroke of luck.
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
The secondary usually has to be grounded somewhere too, with a few limited exceptions. Where you ground this can make a lot of difference what the phase to ground will be.
I think this is why they use 3p wye a lot on 480. It keeps your L/G down to 277.
If you corner ground a delta you get 480-480-0 but if you centertapped it you get 240-240 and a 415v "wild leg".


Greg Fretwell
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
Originally Posted by gscott
Years ago I had to remove all 480V controls from out motor control centers and push button locations. The subject has come up again and I can't find anything that showes this being against code. I have not found anything NEC, NESC or OSHA. Can someone en lighten me on the subject.


You need to look in NFPA79 the standard for industrial machines and in IEEE/ANSI C47xxx the standard for switchgear.
These codes all but prevent any voltage to the door >240V.

Joined: Jun 2007
Posts: 301
J
Member
When you buy a 480 volt combination starter it comes standard with 480 for the stop/start buttons. They use the supply voltage for local control. You have to order and pay extra for a 24 or 120 volt coil and subsequent wiring change on the starter. 480 on PB's are as common as butter on bread.